Evening gents,

I'm just looking for some guidance/clarification on a supply to a summer house I installed. I had to put in a small CU (the existing one had no spare ways left) with a 63A 30mA RCD main switch and a 45A B type feeding the distribution circuit. 6mm2 2 core SWA around a 25m run to the summer house that fed a garage CU with 40A 30mA RCD main switch.

The small CU I put in the house had a Ze of 0.2 ohms and the Distribution circuit had R1 +R2 of 0.33 ohms. The Zs of the circuit/Ze of the garage CU was 0.79 ohms.

Now looking at table B6 in the OSG shows that max measured Zs for 45A b type is 0.82 but I wasnt sure if that includes distribution circuits. Reg 411.3.2.3 states that for a distribution circuit a disconnection time not exceeding 5 seconds is permitted and 411.4.5 says: Zs x Ia < U0

Am I right in thinking that 0.79 x 225A = 177.8 so that it complies?

Apologies in advance for the wall of text and as you might of gathered I'm fairly new to this!

Thanks for your time

Matt
 
The 45A mcb won't discriminate fully with the 20A or possibly even the 6A mcb
The RCDs won't discriminate with each other at all, which ever one has been calibrated to trip faster will do so.
The problem you do have is that you have a 40A RCD supplied by a 45A mcb so the RCD could be overloaded without the OCPD operating

Why ? The circuits supplied by the 40 amp/ 30ma RCD are protected by 20 and 6 amp MCBs respectively , so there's no way the RCD will ever suffer overcurrent.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
TN Distribution circuit to an outhouse
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
Matty7814,
Last reply from
davesparks,
Replies
17
Views
2,180

Advert

Back
Top