I have just carried out an EICR at an old property and found this issue with the main earthing conductor.
It has a TN-S system but the earthing conductor emerging from within the taped up tar coating just before the cut out is only 4mm2 of (what looks like) steel wire armourings. It is 100mm long connected to a small earthing bar. It is not the more popular lead sheathed with earth clamp moulded to it.
My question is, as there is no way to upgrade it without getting involved with DNO cable/equipment, should I just leave the 4mm earth and earthing block close to cut out, then upgrade all earthing from that point on.
Just to point out, at present there is only 4mm earth feeding a BS3036 consumer unit (due for replacement) with 6mm earthing to gas and water. The Ze reading is 0.17 ohms. Adiabatic calculates earth should be 6.19mm2.
Also, what codes for the DNO's undersized earth?
 

Attachments

  • [ElectriciansForums.net] TN-S earthing issue
    IMG_20210109_093124.jpg
    573.5 KB · Views: 121
I do think a 6mm is undersized and needs upgrading just ring the DNO

Why? (in the general case, acknowledging that there are situations where it is clearly true)

Do you have evidence of bare 7/.044 conductors failing to clear a 100A BS1361? Or does a larger conductor just 'feel' more suitable?
 
I give the report to my QS then hopefully he sorts.
So if he failed to act on something you found to be a problem and an injury or fatality was subsequently found to be as a result of something you found would he be the one in court or you

It's the man on the ground that generally cops it as the guy further up the chain covers his back to avoid a stay at one of the HM Hotels around the country
 
So if he failed to act on something you found to be a problem and an injury or fatality was subsequently found to be as a result of something you found would he be the one in court or you

It's the man on the ground that generally cops it as the guy further up the chain covers his back to avoid a stay at one of the HM Hotels around the country
What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.
You’ve noted the observation you may have coded it, then it’s there duty to do the necessary remedial’s,if required.
As an employee you are then asked to do the works,if those works are not assigned to you,that is not your problem.
 
How come?

What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.
You’ve noted the observation you may have coded it, then it’s there duty to do the necessary remedial’s,if required.
As an employee you are then asked to do the works,if those works are not assigned to you,that is not your problem.
totally agree. yous done your bit. reported findings to the decision makers. it's then up to them to act.
 
If the means of earthing is still TNS at the cut out then that’s what I use. If the DNO placed PME stickers on the cut out then they would take precedence. But I’ve never seen this without the change to the means of earthing as well. Any new installation I do as if it will be/become PME.
 
Adiabatic calculates earth should be 6.19mm2.
What figures did you use as I did one this past week with a much higher pfc (2.6kA) and k value of 159 (accessible to touch) for bare copper and works out smaller csa than yours.
You may have used the figure for steel but doubt the dno conductor would be steel, its probably tinned copper.

That aside its worthy of a note (C3 at worst), it meets the adiabatic requirements so all good. The consumers installation starts from the MET put in by the DNO so 16sq from that point! Bonding conductors may be terminated from there or the earth bar in the CU.
 

Reply to TN-S earthing issue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
134
  • Sticky
  • Article
Thank you for getting in touch! Looking forward to use your services in the future! :)
Replies
3
Views
474
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
409

Similar threads

It's not uncommon to find the earth cable put out from the additional neutral knockout, not the designed one on the side. If the rest of it looks...
Replies
2
Views
915

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top