I have just carried out an EICR at an old property and found this issue with the main earthing conductor.
It has a TN-S system but the earthing conductor emerging from within the taped up tar coating just before the cut out is only 4mm2 of (what looks like) steel wire armourings. It is 100mm long connected to a small earthing bar. It is not the more popular lead sheathed with earth clamp moulded to it.
My question is, as there is no way to upgrade it without getting involved with DNO cable/equipment, should I just leave the 4mm earth and earthing block close to cut out, then upgrade all earthing from that point on.
Just to point out, at present there is only 4mm earth feeding a BS3036 consumer unit (due for replacement) with 6mm earthing to gas and water. The Ze reading is 0.17 ohms. Adiabatic calculates earth should be 6.19mm2.
Also, what codes for the DNO's undersized earth?
It has a TN-S system but the earthing conductor emerging from within the taped up tar coating just before the cut out is only 4mm2 of (what looks like) steel wire armourings. It is 100mm long connected to a small earthing bar. It is not the more popular lead sheathed with earth clamp moulded to it.
My question is, as there is no way to upgrade it without getting involved with DNO cable/equipment, should I just leave the 4mm earth and earthing block close to cut out, then upgrade all earthing from that point on.
Just to point out, at present there is only 4mm earth feeding a BS3036 consumer unit (due for replacement) with 6mm earthing to gas and water. The Ze reading is 0.17 ohms. Adiabatic calculates earth should be 6.19mm2.
Also, what codes for the DNO's undersized earth?