I have just carried out an EICR at an old property and found this issue with the main earthing conductor.
It has a TN-S system but the earthing conductor emerging from within the taped up tar coating just before the cut out is only 4mm2 of (what looks like) steel wire armourings. It is 100mm long connected to a small earthing bar. It is not the more popular lead sheathed with earth clamp moulded to it.
My question is, as there is no way to upgrade it without getting involved with DNO cable/equipment, should I just leave the 4mm earth and earthing block close to cut out, then upgrade all earthing from that point on.
Just to point out, at present there is only 4mm earth feeding a BS3036 consumer unit (due for replacement) with 6mm earthing to gas and water. The Ze reading is 0.17 ohms. Adiabatic calculates earth should be 6.19mm2.
Also, what codes for the DNO's undersized earth?
 

Attachments

  • [ElectriciansForums.net] TN-S earthing issue
    IMG_20210109_093124.jpg
    573.5 KB · Views: 121
What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.
You’ve noted the observation you may have coded it, then it’s there duty to do the necessary remedial’s,if required.
As an employee you are then asked to do the works,if those works are not assigned to you,that is not your problem.
So if you if you found the DNO earth had failed or the service head was leaking bitumen or crackling am I thinking you would code it and walk away from site and leave your QS to deal with it!!, surely not.
The book stops at the guy who was onsite not the QS if you code something incorrectly or fail to note something it's not your QS that will be talking to the person in the funny wig if something goes wrong.

As an employee ask yourself would your employer back you up or run away and save his own skin should the **** hit the fan, and the only time you will ever find out is when it happens, Take care
 
So if you if you found the DNO earth had failed or the service head was leaking bitumen or crackling am I thinking you would code it and walk away from site and leave your QS to deal with it!!, surely not.
The book stops at the guy who was onsite not the QS if you code something incorrectly or fail to note something it's not your QS that will be talking to the person in the funny wig if something goes wrong.

As an employee ask yourself would your employer back you up or run away and save his own skin should the **** hit the fan, and the only time you will ever find out is when it happens, Take care
You are now asking a different question,which would have a different coding.
Any code 1 would require immediate action.
Regarding my court case,I’ve done nothing wrong.
 
So if you if you found the DNO earth had failed or the service head was leaking bitumen or crackling am I thinking you would code it and walk away from site and leave your QS to deal with it!!, surely not.
The book stops at the guy who was onsite not the QS if you code something incorrectly or fail to note something it's not your QS that will be talking to the person in the funny wig if something goes wrong.

As an employee ask yourself would your employer back you up or run away and save his own skin should the **** hit the fan, and the only time you will ever find out is when it happens, Take care
i would say that if the DNO earth had failed in some way, you might have a load of C1s or C2s as Zs readings could be unacceptable (although bonding could affect these). You are there to report on the installation,nothing more. Once you have passed that report to the higher ups, and maybe left a copy with customer (all depends on you company's policy) you have fulfilled your remit. Being self-employed myself, the responsibility is with me to advise the customer on remedial work (in writing and signed by customer) and it's then the customer's responsibility to act on it. being employed, it's the employer's responsibility to do this, not yours. Also wsoth noting that we do not have the authority to disconnect any dangerous part of an install, unlike gas. all we can do is issue a danger notice if appropriate. end of the day, it's down to the customer to act/not act on the findings of the report.
 

Reply to TN-S earthing issue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
134
  • Sticky
  • Article
Thank you for getting in touch! Looking forward to use your services in the future! :)
Replies
3
Views
474
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
409

Similar threads

It's not uncommon to find the earth cable put out from the additional neutral knockout, not the designed one on the side. If the rest of it looks...
Replies
2
Views
915

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top