Hi,
I have just completed an EICR on a house my In-laws have just bought (I actually get on very well with them, so I'd like them to be safe)
The EICR was an Unsatisfactory for various other reasons, some of which I will be solving with a CU swap. my main problem is with the Main Earth.
I'm assuming the cut-out is a 63 or 80 amp bs88, I'll call them tomorrow to confirm.
It is a TN-S supply, 0.21 Ze, so clearly not a TT that has had a clamp put on the sheath.
The Main Earth is what looks like 2.5mm² uninsulated stranded steel(?) that is clamped twice (not a bs951, the dno type) onto the outer sheath and another on an inner sheath (unsure of how supply cables are made, but this is the cloth and tar wrapped type, not a modern swa style).
Line and neutral are 16mm² to the meter, 25mm² to the CU (smart meter fitted <5 years I'd guess).
I plan on having an isolator fitted so I can do the CU swap.
So my questions are;
The adiabatic equation tells me it should be a 10mm² minimum. Being that it is a TN-S supply it is their duty to maintain an existing connection IIRC. Should the DNO upgrade this earth for this reason alone?
Who should pay if they upgrade the existing TN-S? Northern Powergrid or customer?
If at all possible to do, would they charge for conversion to TN-C-S and thus provide an earth anyway?
And does anyone have any idea on Northern Powergrid's charge for an isolator to be fitted?
I'm not sure how I've never come across this problem before, I've worked on plenty of CUs with TN-S and TT supplies, but never one in this state.
Thanks for any help
I have just completed an EICR on a house my In-laws have just bought (I actually get on very well with them, so I'd like them to be safe)
The EICR was an Unsatisfactory for various other reasons, some of which I will be solving with a CU swap. my main problem is with the Main Earth.
I'm assuming the cut-out is a 63 or 80 amp bs88, I'll call them tomorrow to confirm.
It is a TN-S supply, 0.21 Ze, so clearly not a TT that has had a clamp put on the sheath.
The Main Earth is what looks like 2.5mm² uninsulated stranded steel(?) that is clamped twice (not a bs951, the dno type) onto the outer sheath and another on an inner sheath (unsure of how supply cables are made, but this is the cloth and tar wrapped type, not a modern swa style).
Line and neutral are 16mm² to the meter, 25mm² to the CU (smart meter fitted <5 years I'd guess).
I plan on having an isolator fitted so I can do the CU swap.
So my questions are;
The adiabatic equation tells me it should be a 10mm² minimum. Being that it is a TN-S supply it is their duty to maintain an existing connection IIRC. Should the DNO upgrade this earth for this reason alone?
Who should pay if they upgrade the existing TN-S? Northern Powergrid or customer?
If at all possible to do, would they charge for conversion to TN-C-S and thus provide an earth anyway?
And does anyone have any idea on Northern Powergrid's charge for an isolator to be fitted?
I'm not sure how I've never come across this problem before, I've worked on plenty of CUs with TN-S and TT supplies, but never one in this state.
Thanks for any help