Hi,

I have just completed an EICR on a house my In-laws have just bought (I actually get on very well with them, so I'd like them to be safe)

The EICR was an Unsatisfactory for various other reasons, some of which I will be solving with a CU swap. my main problem is with the Main Earth.

I'm assuming the cut-out is a 63 or 80 amp bs88, I'll call them tomorrow to confirm.

It is a TN-S supply, 0.21 Ze, so clearly not a TT that has had a clamp put on the sheath.

The Main Earth is what looks like 2.5mm² uninsulated stranded steel(?) that is clamped twice (not a bs951, the dno type) onto the outer sheath and another on an inner sheath (unsure of how supply cables are made, but this is the cloth and tar wrapped type, not a modern swa style).

Line and neutral are 16mm² to the meter, 25mm² to the CU (smart meter fitted <5 years I'd guess).

I plan on having an isolator fitted so I can do the CU swap.

So my questions are;

The adiabatic equation tells me it should be a 10mm² minimum. Being that it is a TN-S supply it is their duty to maintain an existing connection IIRC. Should the DNO upgrade this earth for this reason alone?

Who should pay if they upgrade the existing TN-S? Northern Powergrid or customer?

If at all possible to do, would they charge for conversion to TN-C-S and thus provide an earth anyway?

And does anyone have any idea on Northern Powergrid's charge for an isolator to be fitted?

I'm not sure how I've never come across this problem before, I've worked on plenty of CUs with TN-S and TT supplies, but never one in this state.

Thanks for any help
 
Thanks for the reply darkwood, and the welcome.

I wasn't clear on that point, I'm not specifically after a conversion to tn-c-s. The only time I've ever had the dno out to do work on the service head was when I found an old cast iron cutout and no met, even though the dno said it was a tns and I'd did have an earth. They came out next day and cut the tns cable short and swapped it to a tncs. In the process they upgraded the tails and obviously supplied a MET with an appropriately sized main earth.

Even if someone said it's not the dno to provide an earth in this situation I'll be happy to do a TT. I'm not after a specific supply.
 
There are countless home with a "small" cable from the TNS head to the board. As you have a decent reading I would fit a MET close to the head, then run a 16mm cable from the MET to the CU.

Tin hat firmly on.
 
Maintaining an existing earth is the responsibility of the DNO and they should not charge to maintain this.
Modifications or upgrades to the earthing system may or may not be charged depending on the network situation.

For an installation with an 80A BS88-3 and a Ze of 0.21Ω the fault current would be 1095A causing disconnection in about 0.12s so on an open cable the the csa would need to be 2.66mm² copper equivalent, this is fairly close to the value you guess of 2.5mm² which may mean that the earth is sufficient for purpose. If this is the case then the DNO could well not change it.

An isolator cost is very variable but I would expect less than ÂŁ70 but this is only based on my area which is not northern power grid, the last one I did they provided free of charge because it was asked for, however they told me that unless it was requested they would not fit one. however I think other areas say they will not fit one at all. So in that case you provide an isolator from them to terminate the tails into.
 

Reply to TN-S Main Earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top