Have I got this correct
[FONT=&quot]"It is not permissible to install TN-C-S (PME) systems in petrol stations or large arenas and stadiums, for this reason and for standardisation, all new installations will be TN-S."
[/FONT]


[FONT=&quot][/FONT]
[FONT=&quot]It flies in the face of logic that a PME system is less safe than TN-S, can anyone enlighten me if and why this is true?[/FONT]

[FONT=&quot][/FONT]
[FONT=&quot]Stringbags
[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]
[/FONT][FONT=&quot] [/FONT]
 
In TN-C-S systems, any connection between the combined neutral-and-earth core and the body of the earth could end up carrying significant current under normal conditions, and could carry even more under a broken neutral situation therefore with this in mind; use of TN-C-S is inadvisable in situations such as petrol stations, where there is a combination of lots of buried metalwork and explosive gases.
 
Hi

The HSE banned the use of TN-C-S systems in petrol stations due to the risk of open circuit neutral currents travelling through all the bonded steelwork and the presence of underground storage tanks and flammable gases......little bit iffy!!!!:eek:

Although theres no petrol present at stadiums and arena's and the like, it's due to the presence of all that exposed metalwork coupled with questionable equipotential bonding and corrosion of the joints of the structure, possibly becoming live under an open circuit fault again, bit iffy!!!!:eek:

Another area that suppliers dont like you using their PME is agricultural buildings, again lots of exposed steelwork and questionable bonding.
 

Reply to TN-S or TN-C-S in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
Just a small correction..
    • Like
    • Informative
    • Agree
Replies
6
Views
3K
  • Question
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Thanks James - The earth is TN-C-S. This means the earth is derived from the neutral at my inlet. The DNO live and neutral are disconnected by...
Replies
3
Views
2K
  • Question
It's a bit of a poor job, there's a lot of unsupported cables for starters. With a bit of thought, and some containment it could have been a lot...
Replies
7
Views
3K
davesparks
D
  • Question
You would need to check the cable chosen of course, but for typical 50mm 4C SWA the Prysmian data sheet has 34mm diameter so something like this...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks