Have I got this correct
[FONT=&quot]"It is not permissible to install TN-C-S (PME) systems in petrol stations or large arenas and stadiums, for this reason and for standardisation, all new installations will be TN-S."
[/FONT]


[FONT=&quot][/FONT]
[FONT=&quot]It flies in the face of logic that a PME system is less safe than TN-S, can anyone enlighten me if and why this is true?[/FONT]

[FONT=&quot][/FONT]
[FONT=&quot]Stringbags
[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]
[/FONT][FONT=&quot] [/FONT]
 
In TN-C-S systems, any connection between the combined neutral-and-earth core and the body of the earth could end up carrying significant current under normal conditions, and could carry even more under a broken neutral situation therefore with this in mind; use of TN-C-S is inadvisable in situations such as petrol stations, where there is a combination of lots of buried metalwork and explosive gases.
 
Hi

The HSE banned the use of TN-C-S systems in petrol stations due to the risk of open circuit neutral currents travelling through all the bonded steelwork and the presence of underground storage tanks and flammable gases......little bit iffy!!!!:eek:

Although theres no petrol present at stadiums and arena's and the like, it's due to the presence of all that exposed metalwork coupled with questionable equipotential bonding and corrosion of the joints of the structure, possibly becoming live under an open circuit fault again, bit iffy!!!!:eek:

Another area that suppliers dont like you using their PME is agricultural buildings, again lots of exposed steelwork and questionable bonding.
 

Reply to TN-S or TN-C-S in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top