Took a look at a block of flats today that has a TNC-S supply. Each flat is fed by a 2-core mineral insulated cable. The earth and neutral are then combined again using a henley block prior to entering the consumer unit. Has anyone come across this before?
 
I'm going with no. The 3 phase supply head goes into a ryefield board where it is then split into 60a fuses that feed each flat. See photo below.
 

Attachments

  • [ElectriciansForums.net] TNC-S Supply but combined again at DB?
    IMG_1400.jpg
    521.9 KB · Views: 64
Interesting. I can see why it might be done and that is could be considered safe, assuming the Ryfield board is TN-C-S, but I don't know where the line on ESQCR prohibition of TN-C use is drawn as far as (possible) BNO operations are concerned.

MICC is fantastic stuff, but the high CCC is achieved by running the conductors hot as the 'MI' part can safely and reliably do that, so often VD is the limiting factor on an otherwise unremarkable length. Perhaps it was upgrading flats from historic 40A to modern 60A and someone realised that using the outer copper CPC in parallel with the N conductor would achieve acceptable VD and CCC dissipation limits?

As far as safety is concerned, I see it very unlikely that both the outer CPC and the neutral conductor could become disconnected to present a risk. However, that is still not really dealing with the specific limits on ESQCR & wiring regs on TN-C use.
 
Last edited:
Interesting. I can see why it might be done and that is could be considered safe, assuming the Ryfield board is TN-C-S, but I don't know where the line on ESQCR prohibition of TN-C use is drawn as far as (possible) BNO operations are concerned.

MICC is fantastic stuff, but the high CCC is achieved by running the conductors hot as the 'MI' part can safely and reliably do that, so often VD is the limiting factor on an otherwise unremarkable length. Perhaps it was upgrading flats from historic 40A to modern 60A and someone realised that using the outer copper CPC in parallel with the N conductor would achieve acceptable VD and CCC dissipation limits?

As far as safety is concerned, I see it very unlikely that both the outer CPC and the neutral conductor could become disconnected to present a risk. However, that is still not really dealing with the specific limits on ESQCR & wiring regs on TN-C use.

ESQCR regulation 8 only dictates that a customer may not combine the functions of a live conductor and earth in a single conductor.

It doesn't prevent two seperate conductors being connected together (though I think it should), and it only talks about the "customer" - essentially predating BNOs etc.

I would expect the interconnection of N & E to be prohibited in the connection agreement with the DNO/supplier.

It also breaches 543.4.3 of course.
 
ESQCR regulation 8 only dictates that a customer may not combine the functions of a live conductor and earth in a single conductor.
Ah, an interesting and important distinction between having a a PEN conductor and more generic TN-C
It doesn't prevent two separate conductors being connected together (though I think it should), and it only talks about the "customer" - essentially predating BNOs etc.

I would expect the interconnection of N & E to be prohibited in the connection agreement with the DNO/supplier.
Would be interesting to know when, why, and by whom the linking was done.
It also breaches 543.4.3 of course.
Presumably then the BNO side is under the wiring regs rules and not DNO rules?
 
Can you show the other end of those cables.
Unfortunatly I don't have a photo with the trunking off but this is what was going on:

The MICC is terminated onto metal trunking via a gland. The trunking then had a bolt going through it with a 16mm2 earth fly lead into the consumer unit and another into the henley block containing the incoming neutral.

The main supply prior to the Ryefield is TNC-S.

So the question is... what to put on the EICR?

[ElectriciansForums.net] TNC-S Supply but combined again at DB?
 

Reply to TNC-S Supply but combined again at DB? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
386
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top