Interesting. I can see why it might be done and that is could be considered safe, assuming the Ryfield board is TN-C-S, but I don't know where the line on ESQCR prohibition of TN-C use is drawn as far as (possible) BNO operations are concerned.
MICC is fantastic stuff, but the high CCC is achieved by running the conductors hot as the 'MI' part can safely and reliably do that, so often VD is the limiting factor on an otherwise unremarkable length. Perhaps it was upgrading flats from historic 40A to modern 60A and someone realised that using the outer copper CPC in parallel with the N conductor would achieve acceptable VD and CCC dissipation limits?
As far as safety is concerned, I see it very unlikely that both the outer CPC and the neutral conductor could become disconnected to present a risk. However, that is still not really dealing with the specific limits on ESQCR & wiring regs on TN-C use.