S

swifters

I have a large shed (affectionately known as the warehouse) that is fed by a 16amp rcbo. The main earthing arrangement at the distribution boards is tncs and now a more experienced electrician than myself has stated that the earth in the 3 core 2.5mm armoured cable should be connected to a separate earth rod and make its own tt earthing arrangement rather than be fed back to the main supply, stating parallel paths are the reason. Is he right? Could anyone point to it the new regs book?

many thanks, Jon
 
In that case you need to ensure that you Zdb at the hut complies with the max for the earthing system that you are exporting.

Absolutely and I always do full testing on the outbuilding CU and record Zdb on the test sheet. I don't think that point was ever disputed.

EDIT: They may do, I don't. It's a fair point. I do Zdb + (R1+R2) and then do my ZS tests from the outbuilding. Job done.
 
Absolutely and I always do full testing on the outbuilding CU and record Zdb on the test sheet. I don't think that point was ever disputed.


My point is if the hut is 'too Far',
and you have not done any R1+R2 calculations for the cable,
that you have designed for the expected load,
then how do you know that the Zdb you are going to test after the installation is going to meet the regs?
 
My point is if the hut is 'too Far',
and you have not done any R1+R2 calculations for the cable,
that you have designed for the expected load,
then how do you know that the Zdb you are going to test after the installation is going to meet the regs?

Agreed. However, that is a seperate point from not exporting the equipotential zone at all!
 
In that case you need to ensure that you Zdb at the hut complies with the max for the earthing system that you are exporting.

are you going to calculate the distribution cable R1+R2, and hence calculate the Zdb, as well as the cable size for the expected load? not many do.

or as most people, just design for the expected load and then install the cable, and then take the Zdb measurement afterwards? and hope that it is within the regs?

As they say, a little knowledge is dangerous LOL

they look at max CCC at best and say "it be ite" LOL
 
Agreed. However, that is a seperate point from not exporting the equipotential zone at all!


No it isn't, if you are exporting the EZ, then you must meet the Ze max requirements for the whole system. Other wise, the touch voltages will be above 50V, because of increased Ze.

You have no worries of any sort if the hut is converted to TT.
 
No it isn't, if you are exporting the EZ, then you must meet the Ze max requirements for the whole system. Other wise, the touch voltages will be above 50V, because of increased Ze.

You have no worries of any sort if the hut is converted to TT.

You did not make that point initially though. Your point was a loss of the neutral. This is a secondary discussion. If your ZS does not meet the regs then of course you will have to TT it or take the house nearer to the outbuilding! I do my designing properly and do what is required to meet the regs TBH. BTW, your ZE is at the origin of the supply, not the secondary CU.
 
Last edited by a moderator:
You did not make that point initially though. Your point was a loss of the neutral. This is a secondary discussion. If your ZS does not meet the regs then of course you will have to TT it or take the house neare the outbuilding! I do my designing properly and don't have that problem TBH.

I'm sure you do your designs properly.

but the fact remains, that most of us never calculate the expected Zdb, when we calculate the cable for a load at the end of the garden.

We just go ahead and calculate the cable according to the load, and install and then we test to see if the Zdb meets the system.

Touch voltages are one problem.
Loss of a N at the head is the second.

Loss of N is the more serious, as it leaves all appliances's metallic bodies live,
If this happens at the end of the garden, wet and damp, its a lot more dangerous than in the house.
 
run a 2 core SWA to the hut, an RCd cu in the hut with TT supply from the SWA, and an earth rod at the hut end. SWA earthed at the supply end but the SWA earth insulated at the load end.

What if a gardener/person puts a fork/spade through the cable? Or the cable just detoriates with age? Or there is some other accident that damages the cable.
 
I cannot answer for others and their designing. Before I buy 80 meteres of SWA for their job, I want to know it satisfies the Regs so I don't waste a lot of money getting it wrong!

If the neutral is lost, it is lost. I would not be happy touching any metal part, wet or not! I must also advise people not to use an extension lead plugged in the house (TNCS) and taken all the way to the bottom of the garden either then! We all know they do this too. Common sense prevails here me thinks.
 
^^^^^^ Ze (at origin) + (R1+R2) of SWA submain (for example). There is only one ZE, so if you have a secondary CU in a garage or the like, it is the R1+R2 of the sub main added to the orginal Ze at the primary CU.
 
If you are splitting from a Henley then you do.

If from a CB then you need to stay within the Zs for the CB.

Thats what i was thinking!! thanks

Never though of coming from henley as suppliers would have a fit over 3 metres LOL

- - - Updated - - -

What is the Zdb?

Zs at sub board effectively or calc above :)
 
Sorry to be stupid here but I'm pretty new to this. Why does the bonding conductor have to be a seperate 10mm all the way back to the original installation MET? If you add a rod to the outbuilding and make it a TT system can you not just add a 10mm bond from extraneous parts, to the TT MET in the outbuilding?? More to the point I'm confused as why when you have an original PME system and your supplying an outbuilding, why do I read that the outbuilding should be made into a TT system. Can someone please explain the dangers in lay mans terms and why this doesn't apply if the original installlation is a TT SYSTEM.
 

Reply to TNCS Outbuilding earthing arrangement in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
949

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top