TNCS Outbuilding earthing arrangement | Page 5 | on ElectriciansForums
Discuss TNCS Outbuilding earthing arrangement in the UK Electrical Forum area at ElectriciansForums.net
swifters
I have a large shed (affectionately known as the warehouse) that is fed by a 16amp rcbo. The main earthing arrangement at the distribution boards is tncs and now a more experienced electrician than myself has stated that the earth in the 3 core 2.5mm armoured cable should be connected to a separate earth rod and make its own tt earthing arrangement rather than be fed back to the main supply, stating parallel paths are the reason. Is he right? Could anyone point to it the new regs book?
many thanks, Jon
There is no Regulation requiring out buildings to be TT.
The main reason for considering making an out building TT is simply cost.
Is it cheaper to run a 10mm bonding conductor from the house MET to the out building, or to install an earth rod at the out building?
For an installation with 10mm bonding then I doubt there is much cost difference.
However if the installation needs 50mm bonding and an outbuilding is to have a 32A submain the TT option may be considerably cheaper
Reply to TNCS Outbuilding earthing arrangement in the UK Electrical Forum area at ElectriciansForums.net
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...