Hi all, came to a job the other day, was TNS earthing system also with a rod (TT) has anyone seen this before, test readings Ze and Zs all within TNS limits, maybe the TT was just a back up? If you lose your neutral you’ve lost your earth TNS so can’t really see why there was a rod. If anyone has seen this set up before?
Thanks
 
Possibly a TT that’s been changed to TNS. Nothing wrong with leaving the electrode connected.

I work on a lot of street furniture and TN systems with with earth electrodes are a DNO requirement so it’s more common than you think.
 
I came across such an install a few years ago. The previous owner had long gone, so nobody to question. With the rod disconnect I had a suitable test result for the Ze.

I was concerned though, that perhaps the earthing facility had proved unstable previously. So I contacted the DNO, who sent out an engineer. He said there was no history in the area for earthing problems, conducted his own tests, and I enquired about changing to PME system.

We then went into an unusual discussion, as (he said) the application would take some time, and that the supply at some point between this particular supply and elsewhere, had probably been repaired and changed to PME anyway, so why not do it yourself!

Anyway, after asking advice from my Scheme, I removed the connection to the earth rod, and left it as TNS, with a note & pics on the EIC.
 

Reply to TNS and TT combined in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top