You don't have an earthing conductor there technically, the braid is the DNOs means of earthing which terminates directly into your MET.
The bonds and cpc to the CU then connect to that MET.
In TNS you don't use a table to get your bonding. Your main bonds need to be half the size required for the earthing conductor but no smaller than 6mm and no larger than 25mm.
Would it not be the case that the GY entering the top of the MET is the MEC and is connecting all the exposed conductive and extraneous conductive parts to the means of earthing, ie the DNO braid in this instance.