So
Ipf = 250/0.29
Ipf = 879A
I'll round it up to 900A for simplicity
We also need the disconnection time from appendix 3, which gives us 0.6seconds for 900A
And a value of K of 143 from table 54.2
So for the adiabatic equation we have values of
I = 900A
t = 0.6S
k = 143Hopefully this will make sense!
Yes it makes sense, I'm trying to figure out how you got the value for t.
(1) I know I'm supposed to look up those graphs - but I don't know which one is applicable.
Is it the main protective overcurrent device, or if you don't mind naming the page in appendix three.
Thanks for your patience
TBH I was giving the adiabatic equation (AE)a wide berth - I’m well pleased to be on the verge of understanding thanks to the help on this forum.
The first time I looked at these graphs, I just saw some kind of confusing spiders web.
I’ve sussed how the scales work. I’m posting it up here to check I’m using the graphs correctly.
View attachment 29903
Starting with my 900A PFC on the horizontal axix
Going up to crossing line
Then across to the vertical axis (time)
I’m getting 0.2 rather than 0.6 for “t”, is my methodology wrong ?
Plugging the t value into the (AE) I get 2.8
Taking this further, If I was to check the required CSA of CPC on a final circuit I’d use the Zs rather than the ZE I’ve used in this example ?
TBH I was giving the adiabatic equation (AE)a wide berth - I’m well pleased to be on the verge of understanding thanks to the help on this forum.
The first time I looked at these graphs, I just saw some kind of confusing spiders web.
I’ve sussed how the scales work. I’m posting it up here to check I’m using the graphs correctly.
View attachment 29903
Starting with my 900A PFC on the horizontal axix
Going up to crossing line
Then across to the vertical axis (time)
I’m getting 0.2 rather than 0.6 for “t”, is my methodology wrong ?
Plugging the t value into the (AE) I get 2.8
Taking this further, If I was to check the required CSA of CPC on a final circuit I’d use the Zs rather than the ZE I’ve used in this example ?
Thanks,
Hmmm who carries all those books LOL, unfortunaley I've only got the green and yellow.
Is there anything (an alternative method) like a table in the OSG that would work.
No mate, no dunces hat because you've taught me useful stuff I couldn't understand before. It's my responsibility to check, understand and do my own learning, not to be spoon fed, by good people like yourself and others who help.Based on the above couple of posts I apologise for my above posts which are incorrect. I was basing my calculations on a 100A bs88-2 fuse.
Would somebody please pass me the dunce's hat, I'll be over in the corner.