Hi just checking the main protective bonding conductor size on a tns system, there are two supplys the tails sizes are both (630x2 the supply earth is 240 and neutral is 630x1) persupply
designer aspecified main erthing conductorto met fothe main protective bonding as 2 x 240 i think this i overkill andthe lad on site have installedthis andare putting 50mm forall bonding i think it should be 25mm but looking at table 5.1 in guidence note 8 the table only goes upto 400mm tails
therfore wat size conductor to a: The met forthe bonding, b: The met to the pipework,steel etc
i thnk only nees 25mm