Did a lot of miles today and was pondering.

This is not a real scenario.

Not necessarily "how often does a Ze make an installation impossible?" but more..

If, the measured Ze is say 0.30 Ohms and you then design your installation to keep your Zs's within BBB max allowances, does the DNO have a responsibility to maintain the measured Ze or can they simply state 0.8 Ohms.

For an example you install a 10KW shower.

At time of installation the Ze is 0.3 Ohms.

Your R1+R2 is 0.1 Ohms, Zs of Approx 0.4 Ohms.

10mm T&E on a B50 Zs limit = 0.69 Ohms.

So, job done, cert issued and notified.

Stay with me....

6 months later there's a change of tenancy and the landlord has an EICR done. I nkow

Now the Ze is 0.6 Ohms and my installed circuit is measured as 0.7 Ohms and is listed as a C2 on the cert.

What happens, will the DNO just state "0.8 Ohms not our problem"
 
If the Ze is within stated values as supplied by the DNO I tend to think they will not take any action. Sometimes it is possible to talk with someone and discuss that change and there would be a slim possibility they may check their earth. They are required to maintain the earth as required under ESQCR (24) but whether they would see a legal responsibility to do so in the scenario described I think is remote. And the figures you have shown suggest a change from requirements of .01 ohms so would that be a C2? But anyway the 80% rule applying would mean a significant non compliance I agree. Difficult as to how they would propose to remedy such a C2
 
why are we as sparks so pedantic about things,in my opinion a discrepancy of anything like 0.05 ohms is irrelevant due to all sorts of things ,different meters ,tightness of croc clips, unclean conductor connections etc etc .the dno in my experience would take no action.
 
I've seen 1667 Ohms listed as max Zs on EICRs before where RCDs are present but thought it was frowned upon, relying on an RCD for fault protection.
An RCD is a permitted device for earth fault protection on a TN system, I dont have the BBB to hand for the reg number but it is (obviously) in the section on fault protection for TN systems! and clearly states the maximum Zs in the table for RCD's applies (41.5 off the top of my head ??). A lot of electricians simply dont accept it, but technically, where a 30ma RCD protects a circuit the maximum permitted Zs is 1667 ohms regardless of the earthing system.
 
An RCD is a permitted device for earth fault protection on a TN system, I dont have the BBB to hand for the reg number but it is (obviously) in the section on fault protection for TN systems! and clearly states the maximum Zs in the table for RCD's applies (41.5 off the top of my head ??). A lot of electricians simply dont accept it, but technically, where a 30ma RCD protects a circuit the maximum permitted Zs is 1667 ohms regardless of the earthing system.
411.4.5, 411.4.204, and table 41.5
 
It is not 1667 ohms under the BBB, it is 7667 ohms. 230/0.03=7667
Half agree?
411.4.204 says "the maximum values of earth fault loop impedance in Table 41.5 MAY be applied", not MUST be.
However, I believe the calculation is (230 X 0.95)/0.03 = 7283.3.
But who cares? Never going to get close to any of these values in a healthy circuit.
 
A good question!
I cant imagine the DNO doing anything about a Ze of 0.8ohms on a TNS as its within limits. If it's changed from say 0.3ohms to 0.8ohms which then pushes your Zs over the limit I think that is going to be down to the electrician to sort out. I'm not saying that's fair but it's the only real option.

I also didn't think you could rely on an RCD for fault protection if it is TNS or TNCS. Zs on these systems would almost become irrelevant if we did as they would always be below 1667.
 
Half agree?
411.4.204 says "the maximum values of earth fault loop impedance in Table 41.5 MAY be applied", not MUST be.
However, I believe the calculation is (230 X 0.95)/0.03 = 7283.3.
But who cares? Never going to get close to any of these values in a healthy circuit.
It would be nice if they produced a book that gives clear guidance and limits, maybe review it and ammend it every year or two, it would be costly mind but it would remove the ambiguity.
 

Reply to TNS Ze 0.8Ohms in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top