To spur or not to spur?..... | Page 2 | on ElectriciansForums
Discuss To spur or not to spur?..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
But using that logic if you fitted a 13a FCU right next to a socket which was on the ring everything fed from the FCU would be a spur off a spur etc.?
Yes it is, but think the point is that at least that's acceptable because the cable will be fused down to 13amps, to avoid any overload.
A spur from a spur (even if one of those is a FCU) is not.
The two socket outlets need to be both connected from the fused side of the fcu.
Yes I'm sorry I was visualising this one as the blanked off point being the spur when it's not, but there would be no harm in going off in 2 directions from the outgoing side of the FCU as long as you could connect 4 x 2.5mm T&Es properly within a single box, I'd want a 47mm one for that. :)
There used to be [and still is I think] a picture in the OSG showing sockets via a FCU beig fed in 1.5mm. I wonder if anyone's ever done that ? In theory fine but I like 2.5 or sometimes 4mm in socket terminals.
Fair enough, I do like a bit of 1.5 but normally stick to using it for larger lighting loads or a radial to a small NSH for example. Good for boiler supplies too.
So the majority think it should be both spurs off the load side of an SFCU? That was my initial thought.
The back box is 32mm, but below the surface of the plaster so maybe close to 40. Should be ok for 4 cables.
Sorry if I confused anyone with the set up. I'll draw a diagram next time
1.5mm T&E from load side of a 13A FCU to a 13A socket sounds OK to me.
Here's a thought experiment:
Imagine there was another blank 1G box on the RFC, maybe 3 feet away from your first one. You'd presumably not have a problem having one unfused socket spur from each of these?
Now reduce the distance... a foot apart, still happy?
2x 1G back boxes adjacent to each other (with a part of the ring between them)... Still happy?
How short does the distance between spur points have to be before you become uncomfortable? An inch? You could fit both in the same back box.
What about a length of zero? Two spurs, off the same point on the RFC, using 32A (or higher) 4-hole connectors?
Just a thought experiment :)
Um... I've done the job now. I put the existing spur on the feed side of the SFCU, and the new spur, in 1.5 to a double socket from the load side. Right or wrong, its done now and I cant see the difference from this, or a spur off the back of a single socket and running an extension lead from it.
Reply to To spur or not to spur?..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Luckily when I rejigged the socket to fit the fcu next to it, it meant the original ring wiring reached, i put the socket on the ring and took a...