So today I was installing an extractor fan close to a 2nd DB in a house which was extended about 2 years ago.
This is the nice new shiney CU (and yes there is an EIC for this!) and given I'd viewed the EIC prior to starting, checked the EFLI for the circuit I wanted to add to and I must say I wasn't expecting anything unexpected!!
So I added my spur from the DB for the fan, did the R1 + R2, IR, EFLI and then set my tester to test the RCD..... neither RCD tripped but the power went off...... So I ask the client where the other DB is......
Ah yes, its tucked away and what do I find....
This RCD is after the 1st DB, and on one 40A breaker is supplying the garage PLUS all the MCB's on the 2nd DB, and yes its underfloor heating (a few rooms), a cooker, a hob and lights.
I must say I'm surprised that the MCB for this lot hasn't tripped before and what about the clown who did this lot??
Edit: Yes that is 16mm T & E feeding the 2nd DB which is about 7 or 8 metres away!
I really don't know how people sleep at night - and yes, its a registered Elecsa chap and he lives very close to me too!
The Silver Lining
I've now got to do an estimate to put this lot in such a way that it works properly, PLUS I've done an EICR this afternoon on their soon to be buy to Let, plus the remedials on the flat too.
Thanks to the other chap who clearly is operating as scarper and run!!
This is the nice new shiney CU (and yes there is an EIC for this!) and given I'd viewed the EIC prior to starting, checked the EFLI for the circuit I wanted to add to and I must say I wasn't expecting anything unexpected!!
So I added my spur from the DB for the fan, did the R1 + R2, IR, EFLI and then set my tester to test the RCD..... neither RCD tripped but the power went off...... So I ask the client where the other DB is......
Ah yes, its tucked away and what do I find....
This RCD is after the 1st DB, and on one 40A breaker is supplying the garage PLUS all the MCB's on the 2nd DB, and yes its underfloor heating (a few rooms), a cooker, a hob and lights.
I must say I'm surprised that the MCB for this lot hasn't tripped before and what about the clown who did this lot??
Edit: Yes that is 16mm T & E feeding the 2nd DB which is about 7 or 8 metres away!
I really don't know how people sleep at night - and yes, its a registered Elecsa chap and he lives very close to me too!
The Silver Lining
I've now got to do an estimate to put this lot in such a way that it works properly, PLUS I've done an EICR this afternoon on their soon to be buy to Let, plus the remedials on the flat too.
Thanks to the other chap who clearly is operating as scarper and run!!