B

Boaky

I recently tested a new build (mostly new build) and found 45 sockets on a large ring main in an office environment.
My r1 was 1.6 ohms rn 1.6 ohms and r2 was 2.7 ohms which made my r1+r2 1 ohm roughly
my zs on the circuit was also 1 ohm although I didn't test all of them.
the protective device is a c32 MCB, common sense tells me this is wrong but can anyone tell me why and how to explain it to a spark who has done this twice aslong as me.
No Rcd needed as it's a managed building and all surface work although I would of used a RCBO
 
Forget 'roughly', you need to deal with 'exactly'.

So - what, exactly, was your measured Zs on the circuit? And, what does the BGB say the maximum Zs for a C32 needs to be?
 
I can foresee many potential issues with this circuit, btw, but let's start with what we know......
 
The feed to the DB is 25mm 4 core. Armour used as earth
zs of this board is 0.2
what is BGB. I know I need to be exact but sometimes I not sure to trust my meter even know it's was new this year
 
all depends on the loading of the circuit. worst can happen is the MCB will trip. bad design though. although i don't know of a reg. stipulating max. no. of sockets on a RFC, i consider any more than 15 is too many. should have been 3 circuits, IMO.
 

Reply to Too large a ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
899
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
955

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top