I recently tested a new build (mostly new build) and found 45 sockets on a large ring main in an office environment.
My r1 was 1.6 ohms rn 1.6 ohms and r2 was 2.7 ohms which made my r1+r2 1 ohm roughly
my zs on the circuit was also 1 ohm although I didn't test all of them.
the protective device is a c32 MCB, common sense tells me this is wrong but can anyone tell me why and how to explain it to a spark who has done this twice aslong as me.
No Rcd needed as it's a managed building and all surface work although I would of used a RCBO
 
For r1=1.6, r2 = 2.7, then (r1+r2) = 1.08 Ohm.
If Zs at DB origin = 0.2 Ohm, then Zs for RFC = 1.28 Ohm.
From table B6 in OSG, max permitted Zs for C32 = 0.58 Ohm (the derated value).

I think if you split to 2x 20A radials, you'll exceed max Zs for C20 of 0.93 Ohm
 
Thanks for all the great answers
i originally told them 3 ring mains was the answer but when they questioned me I couldn't really back myself up.
Would a RCBO solve the problem as the max zs would then become 1666
 
Problem is, in office environment, total leakage might be too high either for single RCD/RCBO or for a circuit without high integrity CPC. Even if you can get the breaker to stay in, it's bad design.
 
For r1=1.6, r2 = 2.7, then (r1+r2) = 1.08 Ohm.
If Zs at DB origin = 0.2 Ohm, then Zs for RFC = 1.28 Ohm.
From table B6 in OSG, max permitted Zs for C32 = 0.58 Ohm (the derated value).

I think if you split to 2x 20A radials, you'll exceed max Zs for C20 of 0.93 Ohm

Indeed, if you split it in the middle, your (R1+R2) will double. If split asymmetrically, one radial will be better than that, and one worse.
 
Look on youtube "testing a ring circuit" cant understand your r1,rn,r2 r1 is the resistance of the line conductor r2 the resistance of the neutral conductor, in a RFC wired in 2.5mm singles the R1+R2 reading should be approx 0.5 of your r1 reading, I think you may be testing your RFC incorrectly
 
Look on youtube "testing a ring circuit" cant understand your r1,rn,r2 r1 is the resistance of the line conductor r2 the resistance of the neutral conductor, in a RFC wired in 2.5mm singles the R1+R2 reading should be approx 0.5 of your r1 reading, I think you may be testing your RFC incorrectly

In 2.5mm T&E with 1.5mm CPC, then r2 (for CPC, not neutral) is approx. 1.67x r1.
 

Reply to Too large a ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top