Long time no see and I hope you're all doing well.

I see that torque screwdrivers have become the height of fashion in the UK over the last couple of years. I wondered what general practice has been adopted regarding their use.

Are electricians expected to;
Have a torque screwdriver on site at all times?
Check torque of all terminations in CU's / DB's they open or just any new terminations they make?
Check the torque of all terminations in any accessories they open?

Also;
Is acceptable to do torque testing live in a CU (assuming a VDE screwdriver)? Is a risk assessment required for live torque testing?
If torque testing is performed in a DB/CU do you just check screws for tightness or do you loosen off all terminations first then re-torque to the correct figure to eliminate overtightened connections as well as loose ones?
 
It's a bit like plumbing, you get a feel for it.

I use the same method, tighten up gently making sure no cross threading is taking place, then give it another tweak, and a final tweak before fixing in place.

Usually the third tweak produces nothing in the tightening procedure but gives peace of mind.

I wouldn't trust torque screwdrivers, you might think it's tight because it's torqued to the correct reading, but everything can be faulty.

Good old fashioned feeling can never be wrong, unless you get arthritis.
"When it's white, it's tight"...... (knuckle, for anyone not familiar with the saying!)
 
A related comment about stranded cables.

If you tighten a 6 or 10mm2 conductor as found in twin & earth, if you leave it a while, likely as the strands settle, it will become a bit loose. I'd expect someone used to working with these cables would be aware of that, and recheck tightness after (for example) 10 or 15 mins. But I often see loose connections in shower or cooker isolators, either on an EICR, or after one has failed, and suspect the connections were never checked properly, someone in too much of a hurry to finish.
 
A related comment about stranded cables.

If you tighten a 6 or 10mm2 conductor as found in twin & earth, if you leave it a while, likely as the strands settle, it will become a bit loose. I'd expect someone used to working with these cables would be aware of that, and recheck tightness after (for example) 10 or 15 mins. But I often see loose connections in shower or cooker isolators, either on an EICR, or after one has failed, and suspect the connections were never checked properly, someone in too much of a hurry to finish.

I like to hasten the bedding of stranded conductors, by giving them a wiggle and retightening a few times until there's no more movement.
 
Here's an example... tyre fitters.

They run up the wheel nuts on your very expensive alloy wheels... Then finish them with a torque wrench, set at the correct value.
This ensures that its not too loose, that the vibration of driving loosens them more, and they fall out... nor too tight, as they would damage your alloys.

Its the same type of forces on the screw terminals within a consumer unit. Not too loose, not too tight...You dont want the cable wiggling out... nor do you want the circuit breaker cracking apart because someone turned the driver too much.
Luckily the manufacturers helpfully give you the optimum values.

I would rather see a tyre fitter use a torque wrench on my wheels, that im going to drive away in.... rather than him doing it by 'feel' alone.... using a manual wrench, and him saying "Aye, that'll do"



Don't tell me.... you change your own tyres.....
As we tend to say around here: Get a professional to do it!

Wheel nuts and electrical terminals are different situations.

The torque value for the wheel nuts is set knowing exactly what is being fitted, what its made of etc etc.

Electrical terminals could have a range of types and sizes of conductor put in them, there may even be multiple conductors in there. I can't see how one universal torque setting can be correct for all sizes and types of conductor.
 
A related comment about stranded cables.

If you tighten a 6 or 10mm2 conductor as found in twin & earth, if you leave it a while, likely as the strands settle, it will become a bit loose. I'd expect someone used to working with these cables would be aware of that, and recheck tightness after (for example) 10 or 15 mins. But I often see loose connections in shower or cooker isolators, either on an EICR, or after one has failed, and suspect the connections were never checked properly, someone in too much of a hurry to finish.

The same is true for any fixing which is being tightened to a specified torque setting, it should be torqued, allowed time to relax, and then re-torqued.

For example when tightening down a cylinder head on an engine it's normal practice to tighten to the specified torque, go and have a tea break and then re-torqued to that same setting.
 
Electrical terminals could have a range of types and sizes of conductor put in them, there may even be multiple conductors in there. I can't see how one universal torque setting can be correct for all sizes and types of conductor.
So the torque values published by the manufacturers mean nothing?

I’m sure they’ve done their research and whatever value they state will cover any size, quantity or material of conductor.
 
So the torque values published by the manufacturers mean nothing?

I’m sure they’ve done their research and whatever value they state will cover any size, quantity or material of conductor.

I don't see any claim that torque settings suppled by manufacturers mean nothing.

What has been stated, several times by people who are familiar with the phenomena, is that there are variables which may render those recommendations less than ideal. I'd be amazed if you were to tell me that you'd never had such an experience, that you never check how secure a termination is or that you'd never rechecked a termination and found that it was no longer at the required torque.

Edit: To clarify; my background is originally mechanical and involved regular torquing of components and assemblies which were subjected to fairly extreme pressures. The main variable in those situations were bolts and tie rods, which tended to stretch a little. When clamping several, soft strands of copper it comes as no surprise to me that torquing once and walking away is not an option and that clamping soft copper by various different means may yield variable results.
 
Last edited by a moderator:
I'm with DS on this one when it come s to torquing up and there is an element of twist back / slackening when you first torque up something, and it is good practice to re-torque especially with bigger cores
 
So the torque values published by the manufacturers mean nothing?

No, and that's not what I said!

I said I can't see that one universal torque value could be right for all possible situations.
I’m sure they’ve done their research and whatever value they state will cover any size, quantity or material of conductor.

I doubt that it will, and I suspect that if you asked the manufacturer for further information on this you may find that those torque values are intended for a single copper conductor not doubled back or a fine stranded conductor fitted with a ferrule.
 
25mm tails are a prime example of the torque, tea break, torque, tug test and torque again scenario!
Manufacturer's should have tested all manor of types and sizes of conductor in their device, weather that is the case or not, the entry position and any pressure or bends in the cable will to some degree all have an effect on the final termination, especially with larger cables.
I would rather have some idea of how tight it should be than either trashing the device / terminal or coming loose.
As with most of our work a lot of it is still down to knowledge and experience. If something doesn't feel tight at the required manufacturers setting would you give it a bit more or say that is it that's how tight it should be so f-it?
 
Perhaps there needs to be several ranges based on cable type , bare , ferruled , bent , multi or single etc

That won't happen, if pushed on the issue manufacturers will start declaring that terminals are only suitable for one conductor in their instructions.

We'd end up like the USA where they are not allowed to put more than one conductor in a terminal unless the manufacturer specifically states it is OK.
 
Wheel nuts and electrical terminals are different situations.

The torque value for the wheel nuts is set knowing exactly what is being fitted, what its made of etc etc.

Electrical terminals could have a range of types and sizes of conductor put in them, there may even be multiple conductors in there. I can't see how one universal torque setting can be correct for all sizes and types of conductor.
Spot on.

Also wheel nuts are subject to significant forces and vibration making torque settings important. Whereas Domestic Electrical installations are (generally) not subject to these forces & vibrations, and so terminal screws, if nipped up, are highly unlikely to work loose.

I guess the intent to using torque screwdrivers is a catch all to ensure that "nipping up" is done, which explains the vagueness in the regs and manufacturer instructions.

You simply cannot have a universal torque setting that caters for all cable types.
 
Also to mention some electricians torque screwdrivers only range from 1-3 NM like the Wera , which is a bit naff from a £175 tool when some makes of main switches ask for 3.2-3.4NM
There are plenty of mini-torque wrenches out that that can take screwdriver bits, but fully accept space constraints in some cases.
 

Reply to Torque Talk in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
989
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
Thank you for your response. I really appreciate it.
Replies
13
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top