Please help. I have a basic understanding of electirics, but 5 Electricians are stumped and I don't know where to go next. My mother in law heats her house by 4 Night Storage Heaters, all of which are wired to a Economy 7 supply/fuse board, with no RCD just MCB. The largest of the Night Storage Heaters began to fail and trip the MCD. To cut a long story short, she ended up having a new one fitted. Unfortunately this new one also now trips the MCB. The electricians have tried swapping the various supplies to the various heaters around in the E7 fuse board and the same heater is tripping the different MCB. It would be an obvious thing to consider that there is a fault on the circuit between the board and the night storage heater. However, they have now wired it into the day time board and it is not tripping. Has anyone got any ideas as we need to get it wired back into the E7 circuit??
 
Its a new storage heater as the other one was old and it was thought that the problem was with the old heater. They haven't charged for the new heater as they want to fix the problem before they do. They are willing to return the old heater to avoid unnecessary expense as long as we can sort the problem. So in other words both heaters are tripping the E7 15amp MCB but not the normal board when connected to that.....

Hum .......... this puzzles me - the supplier of the new heater is suggesting you get somebody else to find the fault?

That is bizarre to say the least.
 
I would try and replace the mcb in the E7 DB for a new one, to see if that stays on. Providing the circuit has no faults

The OP has suggested that this storage heater ijn particular trips any of the E7 MCB's .............. so if its not the MCB, or the heater it has to be the cable and / or connections between the 2!
 
I did wonder that too, in particular I've had the older plug in Wylex 'retrofit' MCBs become very sensitive and even 'trip' when the sun heated the porch where they were !
 
Sounds like dead testing shows nothing. What ideally needs to happen is to throw a test on it immediately after it trips this can be done during the day if the electrician is confident enough to energise the E7. One random try is to replace the isolator at the heater, you never know.
 
Murdoch. The same company that supplied the heater are trying their hardest to solve, not asking others to solve. I am seeking suggestions. I think the only thing to do is to fit a new E7 fuse board with RCD. But that still doesn't make sense if all the other heaters work in what ever MCB they are in and to repeat there is no fault with the circuit to the problem heater as it works fine on the normal supply.
 
There's not much to a storage heater, In your case probably 3 elements and 24 bricks.

If they have "fully" tested the circuit, the heater including all the elements and it is ok, then the only other thing it could be is a loose connection somewhere creating a high resistance or what Buzz mentioned, a faulty mcb.
 
Murdoch. The same company that supplied the heater are trying their hardest to solve, not asking others to solve. I am seeking suggestions. I think the only thing to do is to fit a new E7 fuse board with RCD. But that still doesn't make sense if all the other heaters work in what ever MCB they are in and to repeat there is no fault with the circuit to the problem heater as it works fine on the normal supply.

So that wouldn't be a sensible idea .

When the circuit trips, the RCD will shut off ALL the E7 circuits, so your mum will be without any heat..

Its never a good idea to change a fuseboard when there are problems...

If the heater works for a while, then it may well suggest a problem with heat build up in the cable - you state that the heater works on normal rate electricity, but how long did they leave it on for?

I'm guessing that they added a temporary link from the 24x7 board to the cable in the E7 board to said heater? Were you there when this was done?
 
So that wouldn't be a sensible idea .

When the circuit trips, the RCD will shut off ALL the E7 circuits, so your mum will be without any heat..

Its never a good idea to change a fuseboard when there are problems...

If the heater works for a while, then it may well suggest a problem with heat build up in the cable - you state that the heater works on normal rate electricity, but how long did they leave it on for?

I'm guessing that they added a temporary link from the 24x7 board to the cable in the E7 board to said heater? Were you there when this was done?
See #36 and #38.
 
Could be a short on the cable that only occurs when it gets up to operating temperature. IR @500v for a few minutes may show a short somewhere.
 
Please confirm:

Each Storage Heater has its own MCB on the E7 board and all are the same rating?

Same heater will trip any MCB on the E7 board?

You say it's the largest heater which rings bells for me

E7 MCB appears to be tripping a few hours into night storage heater charge. it is not overheating as it does not trip RCD on main board when wired to that.

RCD will not trip if it gets too hot, MCB will!

But it will operate for hours on all MCB's in normal CU?

Are the MCB's in the main CU the same rating as the E7 one?
 
It cant be the cables as they work fine when wired into the daytime supply. I will suggest that the guys to replace the E7 MCB unit's. my hunch is that because its an old E7 unit and the main unit is newer. The MCB's may have failed and are too sensitive and need upgrading, hence the heater not tripping the normal MCB when wired into that.
Thanks everyone who offered useful advice.
 
It cant be the cables as they work fine when wired into the daytime supply. I will suggest that the guys to replace the E7 MCB unit's. my hunch is that because its an old E7 unit and the main unit is newer. The MCB's may have failed and are too sensitive and need upgrading, hence the heater not tripping the normal MCB when wired into that.
Thanks everyone who offered useful advice.
That’s what I’m thinking. Older mcbs in your E7 are more sensitive
 
at first i thought he had put the "faulty" + new heater onto the 24hour supply and that they worked fine, and that this was done at the outlet rather than the db

if this is the case then its the e7 circuit that is faulty, and they have been using the 24h outlet next to the e7 outlet to test, sounds like they do not have the correct test instruments if this is how they are conducting their fault finding

buying new accessories comes after fault finding, not before.
 
That’s what I’m thinking. Older mcbs in your E7 are more sensitive
im thinking the way they have connected the booster+storage heaters into the 24hour supply and it now works

i dont think they have taken the circuit from the e7 board and tried it on the 24h supply

rather they have taken the 24hour supply and put the storage heaters on that circuit outlet

thats all that i can gather/make sense of
 
im thinking the way they have connected the booster+storage heaters into the 24hour supply and it now works

i dont think they have taken the circuit from the e7 board and tried it on the 24h supply

rather they have taken the 24hour supply and put the storage heaters on that circuit outlet

thats all that i can gather/make sense of
The impression I got was that they swapped things at the DBs. The OP doesn’t mention anything about boosters, not all E7 installations have that feature.
 
What is the modal number and KW rating of this storage heater and how is the circuit connected to the 24Hr consumer unit?You state that the E7 consumer unit has 15A MCB's what is the rating of the 24Hr MCB it was put on?
 
either way, something is wrong and should have been figured out on the first visit before changing the heater then backtracing from there

im betting your old storage heater has made its way to the skip, or been crushed beyond repair in the back of a van

the OP is too unclear to make sense of, you need a site visit by a competent sparky
 
Assuming all testing has been carried out effectively and shows no issues. Based on the info the OP has given I would suggest running a temporary new supply cable from the off peak board mcb to the new storage heater and see if it still trips. If it does it must be the heater, if it doesn't it must be the circuit cable.
 
Assuming all testing has been carried out effectively and shows no issues. Based on the info the OP has given I would suggest running a temporary new supply cable from the off peak board mcb to the new storage heater and see if it still trips. If it does it must be the heater, if it doesn't it must be the circuit cable.
a permanent temporary?
 
We all know that the fault is probably quite simple, when found, at least. Until visiting site and having personal experience of the situation, I find some of the confident posts a little presumptuous. I don't tend to criticize other tradesmen without that personal involvement. Sorry if it upsets anyone but let's not presume we're talking about simple cockups (even if we are).
 
We all know that the fault is probably quite simple, when found, at least. Until visiting site and having personal experience of the situation, I find some of the confident posts a little presumptuous. I don't tend to criticize other tradesmen without that personal involvement. Sorry if it upsets anyone but let's not presume we're talking about simple cockups (even if we are).
the replacing of the heater was a bit cart before the horse

it should not take 5 visits to be in the same/worse situation than you started with
 
We all know that the fault is probably quite simple, when found, at least. Until visiting site and having personal experience of the situation, I find some of the confident posts a little presumptuous. I don't tend to criticize other tradesmen without that personal involvement. Sorry if it upsets anyone but let's not presume we're talking about simple cockups (even if we are).
Indeed....I spent 8 hours over 3 visits last week to trace what turned out to be an intermittent lighting fault.
 
the replacing of the heater was a bit cart before the horse

it should not take 5 visits to be in the same/worse situation than you started with
As regards the heater, maybe.....but how do you know it's state, or whether previous tests were or were not carried out.
Five visits seems excessive but how do we know what they involved or how long they took?
 
no a temporary temporary....it'll prove a point. Just chuck a bit of T/E round for a night or two and disconnect the circuit cable feeding the offending heater
is an intermittent lighting fault one that occurs only when switched on but fine if left off. ? :confused::confused::confused:

a farmer i know supplied one of his sheds with steel fence wire, over about a kilometer nailed directly to the top of fence posts

basically a 230v electric fence, cant remember what sort of animal was unfortunate enough to land on said fence but it blew the main fuse
 
a farmer i know supplied one of his sheds with steel fence wire, over about a kilometer nailed directly to the top of fence posts

basically a 230v electric fence, cant remember what sort of animal was unfortunate enough to land on said fence but it blew the main fuse
Would have been fine if the fence posts were taller!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Swansea

Thread Information

Title
Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
216
Unsolved
--

Advert

Thread statistics

Created
Steve Poulton,
Last reply from
Darkwood,
Replies
216
Views
35,922

Advert

Back
Top