Hi all
i'm currently testing a very large office complex on nights. in the boiler house, there are some boilers fed with SY flex. As per usual, the SY braid has not been bonded. When i tried to test for continuity to the braid i found 23v ac on the braid, only with that circuit switched on. is this to do with touch voltages.

firstly, what is this voltage i'm finding on the braid (note. its single phase), is it a capacitive effect and would bonding remove this.
Secondly, i always bond the SY flex yet many people don't. the SY manufacturers make specific glands that no one seems to use. is it a requirement that its not bonded, should i put it on the EICR.

any help would be appreciated
 
I doubt very much it is any form of capacitance by the make of the cable, you have the conductor, surrounded by basic insulation, then you have the outer sheath and then the braid, so highly unlikely it would be that.

As you say if indeed this braid is totally free of earth, then what you have is just a bit of metal floating free, and highly unlikely to be picking up any form of voltage. Sounds like you have a phantom voltage that can often happen with a MFT or electronic voltage tester.
 
What you have to do, is decide whether the un-earthed braid is likely to cause a problem.
When you tested for voltage, I assume that it was between the braid and an earth point?
You have to decide whether the braid is exposed to atmosphere, and whether there is a likelyhood of a spark jumping from the braid to an earth point.
 
Even though sy cable is supplied in mains colours, and it's rated to 600v.

It's designed to be used as a control cable, to which the manufacturer states not for use with mains voltage.
 
Even though sy cable is supplied in mains colours, and it's rated to 600v.

It's designed to be used as a control cable, to which the manufacturer states not for use with mains voltage.
Your wrong it's can be used for mains voltage Rob.
 
Last edited:

Reply to touch voltage help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
268
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
755

Similar threads

  • Question
That's brilliant Dave, thanks again. I had to raid my sons felt tips and pencils for any colours available! Apologies for the strange and...
2
Replies
24
Views
4K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top