G

gamblor6

hi guys. long time lurker part time poster here, job has been done. tn c s earth, outside lights, roughly 30 meters from db. metallic light fittings. should these have there own spike or are they ok with the earth of the armour? im thinkink they are small caravans if you know what i mean.
 
Never really heard or thought of a light fitting being compared to a caravan myself.


Sent from my iPhone using Tapatalk
 
zs was within limits. im just wondering why we cant transport tn c s to a caravan, if we look at bulkhead light fittings as small caravans, far fetched i know, is it within bs 7671 to take tn c s to them? or should i have spiked them? its a sticky subject i know. just wondering what you guys think.
 
The ESQCR regulations 2002 preclude a combined neutral and protective conductor being connected to any metalwork in a caravan, this is primarily because under certain fault conditions, a potential can develop between the conductive parts connected to the PME earth terminal and the general mass of earth.

I wouldn't be concerned with bulkhead fittings however lighting columns set in the ground are a whole threads' worth of debate!
 
as iq says widdler. these are not set in the ground they are fixed to the wall. im not really that bothered but know that way when jobs just bug you, lol.
 

Reply to transporting earths again in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
757
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top