I was on a fairly big new build commercial job recently, nowt too big electrically, but lots of SWA on tray all around the place by the main electrical contractor.
So anyway, I noticed a couple of things they'd been doing that didn't seem right to me, but not really my place to query it at the time, and the lads doing the install had been sound, but just wanted to check my assumption that this isn't how it should be done.
,
1 - None of the tray work had been installed as being continuous and wasn't bonded to the MET or anywhere, ie it just had gaps between one section of tray and the next
2 - All the SWA including some fairly hefty sub mains were just clipped the the tray with pretty flimsy plastic cable ties, so it'd not have a hope in hell of holding it on the tray in the event of any significant fault current, or fire.
The job was a fairly high spec build, at least I thought it was meant to be, so was a little surprised to see this done in this way.
thoughts etc?
So anyway, I noticed a couple of things they'd been doing that didn't seem right to me, but not really my place to query it at the time, and the lads doing the install had been sound, but just wanted to check my assumption that this isn't how it should be done.
,
1 - None of the tray work had been installed as being continuous and wasn't bonded to the MET or anywhere, ie it just had gaps between one section of tray and the next
2 - All the SWA including some fairly hefty sub mains were just clipped the the tray with pretty flimsy plastic cable ties, so it'd not have a hope in hell of holding it on the tray in the event of any significant fault current, or fire.
The job was a fairly high spec build, at least I thought it was meant to be, so was a little surprised to see this done in this way.
thoughts etc?