Does anyone know where i can find the table for tri-rated cable current carrying capacities which incorporate installation methods such as "in trunking".:banghead:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Tri-rated cable CCC. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Can't run any cable at a temperature above that of the connected accessories, so you have to limit the CCC to 70 deg. unless you have 90 or above rated accessories.
Hence why I posted the references I did.
Tri is often actually rated at 105 deg, or at least the stuff I use is.
Sure there is tri rated cable in cu's
If you are not allowed to use 90 deg cables with accessories that are 70 deg cables then why would you use it?
The tri-rated cables we usually use for panel wiring are rated at 90.
Panels aren't governed by Bs 7671 and the tables within it.
I think i've found the answer, according to table 4A3 tri-rated cables to BS6231 come under table 4D1 if installed in conduit or trunking.
eh??? I think we may be getting our wires crossed here.. I'm on about electrical panels with relays, contactors, plc's.... We work to BS7671...
Reply to Tri-rated cable CCC. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net