not in to this sort of thing guys, could someone explain primary and secondary injection?
Many thanks.
Danny

Large ACB’s, OCB’s, VCB’s, Etc have CT’s to give a ratio of the current to the protection instruments. So a 200/5 CT will give 5A to the instrument when 200A is flowing through the main circuit. They also isolate the HV from the instrument.

So to set 200A O/L's at 125% with primary injection a current of 250A would be passed through the primary and the trip time measured. With secondary injection only 6.25A is needed. Further tests would be carried out at higher currents to check the current/time curve.
Now imagine primary testing a 1600A breaker, 125% = 2000A. I don’t even want to think of testing a 6000A breaker.

The primary injection equipment is hefty to say the least hence my reference to ordering a Dr. Scrotes surgical support. An absolute pain to connect up as Engineer said!
 
Last edited by a moderator:
MCB = mechanical circuit breaker? What is the difference to a regular 230V RCD?(new in the game)I presume testing them is a bigger deal than testing RCDs? We test RCDs on the random 230V supplies in trackside cabinets using a Megger IR/RCD tester.
 
MCB = mechanical circuit breaker? What is the difference to a regular 230V RCD?(new in the game)I presume testing them is a bigger deal than testing RCDs? We test RCDs on the random 230V supplies in trackside cabinets using a Megger IR/RCD tester.

MCB = Miniature Circuit Breaker.

The MCB is an overcurrent protective device whereas an RCD (Residual Current Device) only protects against earth leakage and must normally be used in conjunction with an overcurrent protective device or can be combined with an overcurrent protective device, known as an RCBO.

The test currents for RCD testing are typically much smaller (mA) than for MCB testing so the testing is much simpler and the cost of the equipment much less.
 
Last edited:

Reply to Trip Testing for MCBs in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
596
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
774
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
The contacts are pushed open by a cam as the shaft is turned so they operate quite slowly. That's fine on AC as any arc is self-extinguishing at...
Replies
2
Views
994

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top