Sorry stupid me regarding the outside light lol

I put them all in the on position to get my reading.

Just can't understand why it trips after a hour and not when its switched on
 
Yes But I connected them out the circuit etc.

As it happens one of the 2 way switches does not work as it should

Do you think this is the problem ?

It only works if one of the switches is in the on position.
 
Have you tried a clamp meter on the lighting circuit to see what it is pulling (even if all the lights are off) if it is tripping after an hour and is not faulty then it should be taking about 8A.

Then you need to find where there is a cross connection. If there is no RCD protection then between L and N.
 
I had a problem like this once to look at - and set a date thefollowing week to come back.

In the interviening time, the "after a while" became more shorter and by the time I visited switching on a specific light meant the circuit would trip immediately.

The fault was caused the gentle knawing through of the switch cable by a mouse!
 
Had something like this last week, tracked it down to a poorly terminated common cable on a two switch dimmer.
 
Last edited by a moderator:
Have you tried a clamp meter on the lighting circuit to see what it is pulling (even if all the lights are off) if it is tripping after an hour and is not faulty then it should be taking about 8A.

Then you need to find where there is a cross connection. If there is no RCD protection then between L and N.


8A Richard?????
Do you think he is using 240W lamps? :)

To the OP definitely check all terminations, particularly if you think there is too much copper showing - that is indicative of poor workmanship by whoever installed it.
 
Try changing the MCB if tests are ok and no overloading issues....they can fail.
 
Looks like I will be pulling floors up on this one grrrrrrrrrrrrrrrrr


Sounds like a loose connection grrrrrrrrrrrrrrrrrrr


Thanks chaps I will keep you posted.
 
A carbon track is formed when an arc usually caused by dampness between 2 bare conductors.
The track of carbon becomes more conductive with heat until the current being passed takes out the circuit breaker.
This could account for the delay you have experienced.
Not uncommon behind outside light fittings that have not been sealed around connections.
Google it.
 

Reply to the thread, titled "Tripping 6amp breaker" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top