A customer of mine had the same problem, tripping the breaker after an hour. I spent a couple of hours testing IR and used a clamp meter as he switched the lights on one by one. Current crept up to about 4.5 amps with all lights on. Kept the clamp meter in place but it didn't trip while I was there. He was having lots of work done with a new bedroom and bathroom over the garage. The joiner had been putting some plywood down to make a temporary floor in this area. The fault was eventually found by the customer himself after the circuit tripped while he was moving the boards in the working area, and it was due to a cable that had been nipped by the board. I presume this must have breached the insulation to some extent. Anyway it was fixed by cutting out the bad bit of cable. Not quite sure what was happening in the hour leading up to the tripping though. Could the cable be warming up over this time, to cause some expansion of the cable and reduction in resistance of the insulation between line and neutral? Good luck with finding the problem!
 
If it int overloaded, then have a look at the physical condition of the breaker. You will need to take it out of the board to look very closely at it. I had a similar problem a few years ago, and the breaker had a very fine crack in it.

Also is there another breaker that you can put the offending circuit into, to see if the fault moves across?

Cheers........Howard
 
Grrrrrrrrrrrrrrrrrrrrrr

Thought I found it...............

Then when I put back the last light bulb in, it tripped after 5 mins.

The circuits was fine for 6 hours before I put the bulb back in.

1st thing this morning it tripped after 1 hour.

Do you think it could be this circuit that I put the bulb in (the house is damp)
 
mmmmmmmmmmmmm could be the only rose I not looked at (hence last one on the circuit) but would it still trip if isolated at switch (2 way)
 
nobody has yet mentioned the fact that if the MCB is tripping after about 1 hour, it could be a 50% overload. say around 9A. the MCB will stand this for so long, then trip. clamp meter the circuit at the CU and switch all the lights on, see what current is drawn.
 
nobody has yet mentioned the fact that if the MCB is tripping after about 1 hour, it could be a 50% overload. say around 9A. the MCB will stand this for so long, then trip. clamp meter the circuit at the CU and switch all the lights on, see what current is drawn.
Think I may have mentioned that on post 21! Though I did say 8A not 9A
 
It's an old fitting but new bulb.

This one has done me in.

Like I say it was fine for 6 hours then after about 1 hour of me connecting this last bulb in, it tripped.
 

Reply to Tripping 6amp breaker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
152
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
962
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
459
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
896
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top