A customer of mine had the same problem, tripping the breaker after an hour. I spent a couple of hours testing IR and used a clamp meter as he switched the lights on one by one. Current crept up to about 4.5 amps with all lights on. Kept the clamp meter in place but it didn't trip while I was there. He was having lots of work done with a new bedroom and bathroom over the garage. The joiner had been putting some plywood down to make a temporary floor in this area. The fault was eventually found by the customer himself after the circuit tripped while he was moving the boards in the working area, and it was due to a cable that had been nipped by the board. I presume this must have breached the insulation to some extent. Anyway it was fixed by cutting out the bad bit of cable. Not quite sure what was happening in the hour leading up to the tripping though. Could the cable be warming up over this time, to cause some expansion of the cable and reduction in resistance of the insulation between line and neutral? Good luck with finding the problem!