robsparx

did a cu change on friday. tt system, simple split load board, dual rcds. Theres a fault on one of the lighting circuits. when one of the light switches is turned on it trips out BOTH rcds on the CU.

going back to the house shortly to further investigate. would this be a borrowed neutral on the lighting circuit?
 
Hi.

Check the landing light as it sounds like a borrowed neutral where the live comes from the downstairs lighting circuit and neutral from the upstairs lighting circuit.

If there is a 2 gang switch in the hallway i.e 1 for hall light and one for landing light you will probably find the commons are linked, with a T+E going upstairs to the landing light switch and a single core going from the landing switch to the landing light. The neutral is then part of the upstairs "loop in" circuit.

With the lighting split over the 2 RCD's this is seen as an imbalance by both RCD's causing them to trip when it is switched on.

Could also be crossed neutral in CU
 
Its a borrowed neutral.

Or you have crossed connected them in the CU.

Good luck with finding it:)

thought so. definately not cross connected in the cu. finding it on a sunday afternoon is not my idea of fun :(

@lenny. you must be psychic lol. its the landing light thats tripping it out. on a 2g switch in the downstairs hall. supposed to be showing the ELECSA assessor this job tomorrow aswell. wil have to get it fixed tonight :(
 
Last edited by a moderator:
thought so. definately not cross connected in the cu. finding it on a sunday afternoon is not my idea of fun :(

@lenny. you must be psychic lol. its the landing light thats tripping it out. on a 2g switch in the downstairs hall. supposed to be showing the ELECSA assessor this job tomorrow aswell. wil have to get it fixed tonight :(

Had the same borrowed neutral on landing light problem with one of my jobs that was being used on an NICEIC visit.
Sorted it prior to visit which was a must because the nic see borrowed neutrals has a code 1.
Probably the same with ELECSA.
 
still not sorted this. i disconnected the light to stop it tripping out the rcd until i came back, and when i did they said they'd had water come in through the roof and drip through the light overnight. lucky i'd already disconnected it. So i've left it how it is until the roofs sorted.

they dont seem keen on having to have rewiring done though
 

Reply to Tripping out BOTH RCDs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
500
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
352

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top