You are doing a barn conversion 45m from an existing supply and taking 80A off that supply. Are you sure that the existing will take the additional load?

It is a new supply for the Barn Conversion so has no other load. I did recommend to the client to have the new supply put in straight to the Barn but he didn't want his driveway (mud and a few cobble stones) dug up! I have done the cable calcs and it came up with 35mm so I am putting in 2 Core 35mm SWA buried 600mm down.
 
Re: TY Distribution Best Practice

No it doesn't require RCD protection, if the Ra of the earth electrode is sufficiently low enough to allow the OCPD to operate.
However, as that is probably not going to be the case, then an RCD is the only option to achieve the required disconnection times (1s for TT distribution circuits).

Thanks spin , I was starting to think i was losing the plot and had been doing it wrong all this time !
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TT Distribution Best Practice
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
owenskinner,
Last reply from
JD6400,
Replies
16
Views
3,416

Advert

TrueNAS JBOD Storage Server

Back
Top