R
richiek
Hi all, just heard about this forum and decided to give it a go.
I've only been a sparky for just over 2 years and last week a mate of mine who's a general handyman fitted a 12v door bell for a lady which is mains fed to a transformer. He wired it into a JB on the lighting circuit in the loft but called me as he noticed when he was touching the earth terminal with one of those harry tate screwdrivers that light up the light inside was flickering. I went round and put my fluke voltage tester across neutral and earth and sure enough there was a slight voltage there instead of the usual continuity. It was only very slight - prob less than 1v - but shouldn't be there nonetheless.
I carried out an earth loop test which read OL before eventually tripping the RCD as my Robin multi-tester doesn't have d-lock. I noticed she had a TT system and eventually located her earth rods concreted into her basement. They looked quite old and could be coroded so I guess this would be the cause of the earthing problems. Her entire consumer unit is RCD protected and I tested this and it trips in good time (19-29ms). Her next door neighbours have the same system which is also quite old but they don't have an RCD protected board, instead they have an old VOELCB which to be honest is a waste of space. They also have this problem of minute current in the earth but when I tested their earth loop I got a reading of 13.8 ohms which aint bad on a TT in my experience.
What I'm wondering is, would it be worth going through the hassle of replacing this lady's earth rods as she's well protected by her RCD and her existing ones are concreted in? They may even be connected to an earthing plate under the concrete. Would replacing them be guaranteed to cure this problem?
Any thoughts any of you more experienced guys?
I've only been a sparky for just over 2 years and last week a mate of mine who's a general handyman fitted a 12v door bell for a lady which is mains fed to a transformer. He wired it into a JB on the lighting circuit in the loft but called me as he noticed when he was touching the earth terminal with one of those harry tate screwdrivers that light up the light inside was flickering. I went round and put my fluke voltage tester across neutral and earth and sure enough there was a slight voltage there instead of the usual continuity. It was only very slight - prob less than 1v - but shouldn't be there nonetheless.
I carried out an earth loop test which read OL before eventually tripping the RCD as my Robin multi-tester doesn't have d-lock. I noticed she had a TT system and eventually located her earth rods concreted into her basement. They looked quite old and could be coroded so I guess this would be the cause of the earthing problems. Her entire consumer unit is RCD protected and I tested this and it trips in good time (19-29ms). Her next door neighbours have the same system which is also quite old but they don't have an RCD protected board, instead they have an old VOELCB which to be honest is a waste of space. They also have this problem of minute current in the earth but when I tested their earth loop I got a reading of 13.8 ohms which aint bad on a TT in my experience.
What I'm wondering is, would it be worth going through the hassle of replacing this lady's earth rods as she's well protected by her RCD and her existing ones are concreted in? They may even be connected to an earthing plate under the concrete. Would replacing them be guaranteed to cure this problem?
Any thoughts any of you more experienced guys?