A friend of mine has a garage which is powered from an FCU on a ring final from his house, the garage is a little way from the house and is a TT earthing arrangement (the house PME earth is terminated in a plastic wiska box (where the SWA cable is terminated) and isolated from the garage earth), it then runs around the garage to a few socket outlets the earth rod is underneath the furthest outlet and has 10mm earth cable running back to the wiska box where there is a small MET on the wall just above it.
The 10mm earth runs a different way than the conduit for the sockets and he is having some brickwork repaired and a new door fitted so needs to remove the cable temporarily although he has asked me if he would be able to take the earth cable into the last socket directly above it instead of going back to the MET, this would then connect the earth rod to the CPC for the sockets, although terminating a 10mm in a socket may prove tricky, as the sockets CPC is 1.5mm then can the earth rod cable be a smaller size.
Currently, the earth rod is connected to the MET with 10m which runs around the garage then there is 1.5mm cable also terminated in the MET from the T&E from the sockets, so the MET is just taking the 10mm down to 1.5mm effectively
I am not quite sure if this is alright or not etc, I know its not the best way to get power to a garage but that was already there.
Thanks Marcus