TT earthing on a rewire | Page 2 | on ElectriciansForums
Discuss TT earthing on a rewire in the UK Electrical Forum area at ElectriciansForums.net
J.C.E
Earth
Evening men!
Looked at a upcoming rewire
it is for a mid terrace old house.
A single phase comes into the house next door- one 60a head in next doors house >>meter>>cu
Then a 2nd feed goes into the house I am planning to rewire into a 60a head>>meter>>cu
I have seen this before- but what concerns me is the earthing
it is just a bonding clamp around the incoming servive- then into a met in each house
so a TNS
however upton getting a quick ze reading it was 4.3ohms- likely to be loose clamp
The builder got UKPN out and they said this to him:
"Single supply to no17 with a link to no 15 through the wall as we knew.
When Installed by London Electricity Board 50 or so years ago no earth was provided. UKPN having adopted the network will not and do not provide an earth where it is not present such as on a TT supply like this one.
The earth next door is not fitted or owned by UKPN (nor is the link between 15 and 17 oddly but they do own the head in 15...) If the steel pipe that covers the lead insulation of the supply underneath is in good contact and the pipe is very clean of rust under the earth bonding it could be a good earth. If its not it wont be.
2 options.
1- New Supply - PME.
2 - Earth Spike"
the client can not afford a new PME supply
If I go down the route of install a rod and making it a 'offical' TT system do I need a upfront RCD
they want the c/u remote from the meter so it will go meter >> sw isolator>> cu via 3c SWA
the consumer unit will be dual 30ma rcd
do I need a upfront 100ma rcd to cover the SWA sub main or am I over thinking again!
So put a temp board in for this job this morning.
2meter of rod into ground with 16mm earth into MET
100ma time delaying RCD+ fuse carried combo (used PROTEK as wholesaler stocked it)
into a temp board
I got a live Ze reading (test meth 2) as I do not have a electrode tester
The reading was supprising 3.05ohms (I was expecting alot higher for 2m rod!?)
but it did go down pretty easy so guessing the ground was nice and soft
1)on my easycert form what is the 'resistance to earth' reading?
2) what is the 'rated time delay in ms' value- doesnt say on the protek rcd which is model 'T80-100-2TD'
Hi - that is very good and that's your number.
For rated time delay - it depends on which standard the RCD was made to. If you've got your OSG the info is in chapter 11, p112.
That reading obviously goes into 'measured Ze value' but does it to go in 'resistance to earth' box too?
Reply to TT earthing on a rewire in the UK Electrical Forum area at ElectriciansForums.net
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
loz2754
L