Can anyone help. Me and my boss are currently doing a full wiring job on a barn conversion. Due to the location of the barn, a TT system has been used. There is an earth rod outside with a 2mm cable running to it. We ran a test yesterday and got a result of 368 ohms, been used to working on domestic installations we are under the impression that you need a result of under 0.7 ohms to pass. Is this correct?
Today we have installed 2 x 4ft rods and upgraded the earth cable to 16mm, we are yet to test it but my boss is not holding out much hope of it been much lower. I did a search on here and a few people have mentioned that the reading should be inder 2000 ohms!!!! If this is the case we are well under with our 368 but am I misunderstanding the regulations?
Does anyone have any experience of TT rural installations or know the exact requirements.
Sorry to be a pain and thanks in advance.
Forgot to mention that on the old installation there was a 60A fuse to the meter, then connected to a crabtree ELCB, however we are replacing this to a 100A fuse via the local supplier and changing the ELCB to a 100A Isolator, we are then installing 2 Proteus CU's will full RCD protection except for the boilers.
Due to high Ze readings on TT systems, are we conforming by making everything RCD protected? If so are we breaking regs by leaving the boilers (x2) unprotected?
Today we have installed 2 x 4ft rods and upgraded the earth cable to 16mm, we are yet to test it but my boss is not holding out much hope of it been much lower. I did a search on here and a few people have mentioned that the reading should be inder 2000 ohms!!!! If this is the case we are well under with our 368 but am I misunderstanding the regulations?
Does anyone have any experience of TT rural installations or know the exact requirements.
Sorry to be a pain and thanks in advance.
Forgot to mention that on the old installation there was a 60A fuse to the meter, then connected to a crabtree ELCB, however we are replacing this to a 100A fuse via the local supplier and changing the ELCB to a 100A Isolator, we are then installing 2 Proteus CU's will full RCD protection except for the boilers.
Due to high Ze readings on TT systems, are we conforming by making everything RCD protected? If so are we breaking regs by leaving the boilers (x2) unprotected?