Right then....
I think im going to take out the board and fit a metalclad unit - 100ma main sw and 8 30ma rcbos. 3 rings and 2 lighting and a pv feed all on independent circuits.
An amendment 3 consumer unit would seem sensible in a agricultural location so long as the tails are protected. The main switch should be a time delayed version.
From the document to which you linked I might replace the 30mA RCBO on the PV with an MCB, assuming (since it is on 100mA at the moment) that the circuit cables do not need 30mA RCD protection.
Stake it and bond. Park the core used for earth and armour into a plastic box.
Not definite what you mean by stake and bond, if you mean provide an earth rod and ensure main and supplementary bonding is in place and effective then yes.
Divorcing the incoming earthing system is critical.
I want to try and do the stake in the room where the board is - and go deep as 15ft.
Earth rods inside buildings are not often good as the foundations and the lack of surface water can render them limited in stability and effectiveness but a 5m rod could well overcome this.
Ill install 2 circuits on independent rcbos - one for sockets and one for lighting for the yard.
Again I am unsure about your meaning here but from the above posts you are intending to have a separate board for these circuits. I think you are doing this to avoid total loss of power if the 100mA S switch trips. Yeah you can do that.
That's the plan of attack.
Still unsure about the pv tho - currently fed through a 100ma rcd. I cant see a issue if i put it on its own rcbo but i don't know enough to make a call on it.
If the inside rod proves rubbish - its a concrete pad of 18in id be going through - ill move it outside but then id be cutting out the slab etc to run the wire and want to avoid this if poss - horses afoot.
They have said nobody would stay above as access is a mare - scuse the pun - so i can take dwelling out of it but saying metalclad as it'll be nicer to use with my conduits.
Anywhere i may fall short?
The ideas of the plastic board was to save client some money but may as well go the whole hog - his spec was to make it bombproof lol
See my comments above, the inverter you specify does not of itself require RCD protection, but RCD protection is required for ADS on a TT, therefore 30mA RCD protection would seem to be overkill.
I would not select an indoor location for an earth rod, but you know the layout of the site.
This is the layout on which I have based my comments.