If your installation is in a sorry state, be aware that the lighting circuits, if they are up and down, woulld ideally be on seperate rcds This may become a problem with imbalance of the rcds if there is a shared neutral
Just a word of caution not to have to sudenly come up against this problem when changing consumer unit
 
6mm2 is the minimum size for the main protective equipotential bonding to the Gas service pipework on a TT system..although this only usully applies if the Main Earthing conductor is no more than 10mm2,,,,,,,on TNCs supplies the minimum bond is 10mm2
 
Lots of deals on CU's eg screwfix do a 10way split rcd wylex for £97.86 inc free x5 pendants & x10 dbl sockets.
Regards
Kung
 
Thanks for all your replys . I have purchased a 17th edition dual rcd CU today.

I have run the main earth to the earth rod , run the main equipotential. Floor boards up every where lol.

Had a look and the old CU and notocied that the lighting circuits still wired in old rubber cables :eek:
Thought thats strange as changed a few light fittings and never noticed them before.
checked all light fittings and their wired in T& E and all the switch wires are as well except for the one in my bedroom which is rubber.

Some ones been very naughty:mad: i will have to pull up a few more floor boards and find were its joined. Oh and looks like a bit of chasing out and replacing that switch wire.

I'am so lucky didn't want to put my feet up any way.:)

Mark
 
Hi Mark,

That old rubber cable needs to come out, as you are doing.

Perfectly fine in its day but it would have aged and will be starting to break down.

That would give your IR test some hell:D
 

Reply to TT Installation in need of some TLC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
499
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
I am with you. Their RCD did not comply with the standard. The only one I know that does comply, though I am sure it isn't alone, is the Garo...
    • Like
Replies
10
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top