I don't think you'll find a 25V touch voltage stipulated anywhere in BS7671:2008

To be honest I cannot remember where I came across a 25V touch voltage, it may have been when I did a stint panel building/assisting in testing, possibly a panel for the gas/petroleum industry or medical ?, I had it in my mind possibly for swimming pools, but a quick look at the regs suggests otherwise.:smile5:
 
Last edited:
dont farms have a 25v touch voltage​

I had a quick look through GN7, and it suggests <= 50V, but I haven't had an in depth search of the Regs.

Iam racking my brains to try and remember where I came across this, unless it was for a 'specific requirement' over and above the Regs. but Pass ?, or as you say in an earlier edition of the regs.
 
Last edited:
No probs mate...Sorry about that TQ Will have to read the post a bit clearer next time lol......:smile5:
Sorry mate, I didn't see this. No need for apols. I usually read the whole thread through first (and can forget what was said by whom). I should go back and read the OP again (which I normally do after posting to ensure all the questions have been answered) then often realise I've misunderstood the OP entirely :banghead:.
 
I had a quick look through GN7, and it suggests <= 50V, but I haven't had an in depth search of the Regs.

Iam racking my brains to try and remember where I came across this, unless it was for a 'specific requirement' over and above the Regs. but Pass ?

Lol, I wasn't guessing when I said it was deleted from BS7671:2008 ;)
 
This was why I joined this Forum, you cannot beat older, wiser and more experienced guy's for advice, as none of us know it all.:tounge_smile:
 
Last edited:

Reply to TT Max ZS loop reading for circuits over 32A in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
889

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top