Iam purposely avoiding looking at the BGB (although I have it), because Iam still trying to get on a 2391-10 course in around September, and don't want to end up mixing the regs between the BRB, unless anyone can advise differently.

How I wish I did this when I was younger, instead of contracting for short term gain.:33:
 
Last edited:
I haven't got the BGB in front of me but I'm pretty sure I eye-balled the 25v a.c. touch voltage in section 710 (medical locations) in groups 1 & 2
 
HI all anyone know the above, i put 1667 ohms in the box normally for all TT circuits but noticed the other day it is only for circuits upto 32A

Anyone enlighten me, i need it for a 50A and 40A circuit??

thanks
In the BGB, the words 'for final circuits not exceeding 32A' have been removed from the heading of Table 41.5.
They've also removed the other voltages from the table, leaving just 230V.
 

Reply to TT Max ZS loop reading for circuits over 32A in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
889

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top