When filling in EIC for a TT system do I put 1667 ohms in the box for max allowable Zs. For every mcb that is protected with a 30ma RCD
 
chapter 41 of BS7671 has a table not sure i think its 41.1 for disconnection times also look at the 2 top regs of the next page fro Dis circuits and circuits not covered byt the table
 
Can you help me with two questions. What is the max disconnection time permitted.? And max Zs permitted.?

If you are still referring to a TT system the disconnection times are 1s for distribution circuits and circuits not rquired to have additional protection via 30mA RCD & 0.2s for all others.

There are notes to these times so as Tom said best to read up on pages 46 & 47 of ol' red.
 
don't want to hijack this thread but didnt see the point in starting another, I have looked at table 41.1, what would you put if the rcd was time delayed as well? The problem I have is for a TT system to some prefab office units, the rcd that protects them is one of the variable type used on building sites, from 100ma upwards and with a variable rcd with time from 0.25 to 1 second. (it is set at 300ma for 0.25 seconds) The cable from this feeds a tp&n board (with no additional rcd) which in turn feeds each bay (via a 60898) that has a 30ma rcd protecting all circuits. I am filling out the sheets for the circuits that feed each bay and need to put in the max zs. The overcurrent device is a type b 60898 50a which gives an 80% max zs of 0.73, the Zs measured due to TT was 46ohms. Do i put 153 (230-400v 300ma it is protecting a tp&n boar but the circuit itself is single phase) or 167 (120-230v 300ma). Ordo I go and boil my head cos I am making it harder than it needs to be!!!
 
I would record the lowest value in this case 167ohms, for the highest setting of 300mA.

As you have a pretty good Ra of 46ohms the 300mA RCD will disconnect in the required time anyway should a fault occur upstream of the 30mA RCD's which will also clear any fault downstream before the volatge rises above 50V as the max permitted for them 1667ohms.
 

Reply to TT max Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

Thanks for that, good line of thought. My take is that safety is about protection of life/people/livestock hence the earth thing and protection of...
Replies
31
Views
2K
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
379

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top