hi
just been to a house in Rhyl. the occupants were getting shocks from the sink.
Its TT and i found out it had just been rewired.
there was no connection to earth, no rod and no equipotential bonding!!!

We fitted a rod and bonded everything. i got a Ze of 25.1 ohms after we did the work.
im going back tomorrow to do a EICR.

Are 100ma RCds still required? they have got a 16th ed split load board. half circuits on 30ma rcd, other half just MCBs.

also, for TT is the max Ze 200 ohms.

any help and guidance would be helpful...in 8 years of testing its my first TT!!!
 
So if this is your first time for installing/creating a TT system, how did you install, what size, and how deep did you drive the rod(s)?? Did you provide a flush to ground earth pit/chamber to protect the rod/conductor connection??
 
Last edited by a moderator:
every circuit within a TT system should be RCD protected i personally doing a job on a TT system today would use a current 17th edition split rcd consumer unit. A reading of 25ohms in for an earth rod in these dry conditions is good and i would expect it to be lower in wetter weather. 100ma rcd protection on lighting circuits although not to 17th edition (asumming cable buried) would be advisory to change to 30ma. TT systems are easier to understand and work with, than people think. When you dont encounter them and come across one the immediate fear kicks in but if you step back use you knowledge follow the regs/OSG they are straight foward although the zs/ze results can be different on any given day!!!
 
So you installed a single 1m rod?? ...Do you and your boss think that the single rod is going to be a stable earth electrode?? Stability comes with depth, and i would always advise you couple a minimum of 2 X 5/8'' (16mm) extendable rods on any domestic TT installation.

Good to know a flush earth pit was included in this install though!!
 
Why is there a 16th Ed board on a rewire?
No earthing?
Sounds like the customer got stiffed by the sparky? Are they Welsh and was the Spark English :)
 
Loads of tt's round me. all in the regs... Not many earth pits.. not entirely essential.. Into most ground 1 mtr rod is fine (depending on install...) I got a rod stuck 200mm in one day. Thought I would test it.. Same reading as the 1 mtr rod i put in next to it...

Cant believe the no earth install.. And in this sort of case agree with the Electrical Trainee generation.. :smilewinkgrin:
 
That house had not been rewired it had been made deadly!

If you have a 16th edition board then the half without 30mA RCD protection does not meet the TT requirements for all circuits to have RCD protection so you would need an upfront 100mA RCD or the like. A nicer solution would be to replace the single RCD board with at least a dual RCD board or fit RCBOs; so long as the supply circuit does not need RCD protection.

The regulations state that a Ra value above 200 ohms may not be stable , though as you have heard from E54 this is potentially a misleading statement.
a stable reading is key and if you believe that will be obtained from your current rod installation then this is OK. I would say 25.1 ohms is fine for a Ze reading for a TT, but you would need the RCD protection to get the disconnection times for earth faults.
 
Cant believe the no earth install.. And in this sort of case agree with the Electrical Trainee generation.. :smilewinkgrin:

Bit of a sweeping statement isn't it without the facts? May as well blame women or hamsters? Could have been an old die-hard sparky, past his prime that won't update, else could have been a plumber 'pretending' to be a sparky?
 
Bit of a sweeping statement isn't it without the facts? May as well blame women or hamsters? Could have been an old die-hard sparky, past his prime that won't update, else could have been a plumber 'pretending' to be a sparky?

I can assure you,I had nothing to do with the job
:smilewinkgrin:
 

Reply to TT-no earth rod in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top