just been to a house in Rhyl. the occupants were getting shocks from the sink.
Its TT and i found out it had just been rewired.
there was no connection to earth, no rod and no equipotential bonding!!!
We fitted a rod and bonded everything. i got a Ze of 25.1 ohms after we did the work.
im going back tomorrow to do a EICR.
Are 100ma RCds still required? they have got a 16th ed split load board. half circuits on 30ma rcd, other half just MCBs.
also, for TT is the max Ze 200 ohms.
any help and guidance would be helpful...in 8 years of testing its my first TT!!!