TT off water main or tncs with no earth (Victorian house city centre)

Hi guys came across this today, Ze of 37 ohms, surprised me as thought it was a tncs- Victorian house, Db from 1989, no docs- could it be a TT off the water main? 10mm bonding to gas and another 10mm out of sight. The met on the rhs of tncs
block not connected to neutral- can anyone help me with some ideas? Cheers.
IMG_20180228_104819916.jpg
IMG_20180228_114411875.jpg
 
Hard to tell from your pic, set up would suggest TT. Have you followed the route of the EC and see where it terminates, the head looks like PME, have you asked the DNO?

Just re-read your post, you say the earth is not connected to the neutral link?
 
Hard to tell from your pic, set up would suggest TT. Have you followed the route of the EC and see where it terminates, the head looks like PME, have you asked the DNO?

Just re-read your post, you say the earth is not connected to the neutral link?
Try to get a PME terminal from the DNO or you could drive a new spike in directly below in the sub floor and convert to tt system,
then sell them a new board.
 
EV disappears below floor to back of house possibly to water main. Rang DNO, they were not helpful- have to wait for an appointment. Earth not connected to neutral- inside the block, seals already broken. Checked neighbour's, his is the same but neutral connected to earth inside the block - looks like his is tncs and he had a 0.54 Zsat the kitchen ring..
 
EV disappears below floor to back of house possibly to water main. Rang DNO, they were not helpful- have to wait for an appointment. Earth not connected to neutral- inside the block, seals already broken. Checked neighbour's, his is the same but neutral connected to earth inside the block - looks like his is tncs and he had a 0.54 Zsat the kitchen ring..
Any sticker on the neighbours? ;)
 
It was common practise many moons ago to use the pipe as means of earthing . You still can with the owners permission which would be a pain to get and unreliable as pointed out,with constant upgrading etc.to plastic

It was common up here as there are a lot of TT systems .
A lot were in the colliery housing areas , the replacement plastic pipes left the old cast pipes intact , usually under the gardens , so fairly safe until the houses are demolished .
The last one I worked on many years ago the RA was 6 Ohms.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
James Kinrosd,
Last reply from
BOYD BARKLEY,
Replies
54
Views
7,179

Advert

Back
Top