TT off water main or tncs with no earth (Victorian house city centre) | Page 2 | on ElectriciansForums

Discuss TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 2, 2017
Messages
14
Reaction score
1
Location
London
Hi guys came across this today, Ze of 37 ohms, surprised me as thought it was a tncs- Victorian house, Db from 1989, no docs- could it be a TT off the water main? 10mm bonding to gas and another 10mm out of sight. The met on the rhs of tncs
block not connected to neutral- can anyone help me with some ideas? Cheers.
[ElectriciansForums.net] TT off water main or tncs with no earth (Victorian house city centre)
[ElectriciansForums.net] TT off water main or tncs with no earth (Victorian house city centre)
 
Many thanks for your replies guys! Even if left as is, or with an additional earth spike, am thinking the board would have to be updated to protect the circuits on the right hand side that only have a 100ma RCD to bring them under a 30ma RCD.....
 
Many thanks for your replies guys! Even if left as is, or with an additional earth spike, am thinking the board would have to be updated to protect the circuits on the right hand side that only have a 100ma RCD to bring them under a 30ma RCD.....
 
It was common up here as there are a lot of TT systems .
A lot were in the colliery housing areas , the replacement plastic pipes left the old cast pipes intact , usually under the gardens , so fairly safe until the houses are demolished .
The last one I worked on many years ago the RA was 6 Ohms.
Innovative more than informative, rus. I like that.
Common sense really, though, as you say.
 
Yes ' The death of common sense ' lol.
The ground was so wet around these houses anyway even with rods the readings were quite good. They are still standing and in use to this day.
Not by Miners though . ( cap intended) :)
 
What is the earthing block to the rh side of the cutout?
The cutout is just one of the solid n e ones which doesn't require a link. That cannot be taken as an indication that PME is available
 
I had a dodgy homemade tns the other week with a Ze in the kilo ohms. DNO came out, officially declared it was never a tns (probably was in reality, should check a few neighbours maybe) and that I should TT it. Very decent initial Ra of 11 ohms from one rod, with a Zs that dropped to 1.35 ohms ish on a B32 with the water bond. I am very tempted to bang another rod in to see if I can bring the Zs's down further, albeit with a lot of thanks to the water supply pipe!
 
It goes on to say that other metallic water supply pipework should not be used as an earth electrode unless precautions against it's removal and it has been considered for such use.
 

Reply to TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
429
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top