Just been to look at a job and found this. It's an overhead supply so could be pme at the post but no earth back to the cutout and (although admittedly i didn't have much time to have a proper look) I didn't spot a rod.
I'm thinking advise the customer to get the dno to come and have a look and fit an isolator while they're at it.
Any thoughts?
Thanks!
I get what you are saying...
I'm guessing the earth rod would be too high resistance to prevent the issues in the event of a broken PEN?
Therefore it would seem sensible to disconnect this cable from the CU and safely terminate? But this presents new issues with having a green and yellow cable that I suspect is tied to the incoming Neutral hanging in the wall.
If it is what you think it is, and a loss of PEN should occur putting 230 onto your earthing, the earth stake is unlikely to worry the service fuse
I'd be inclined to try to see exactly where this mystery conductor goes, I think a parallel path through neighbouring property etc is far more likely than some weird DIY extraneous CNE connection
OK so I have been round for a while today to get some more clarity and attempt to trace this cable.
Managed to trace the cable into the bathroom, through a bedroom then it seems to go down towards the kitchen and is buried in a wall so can't trace it further than that.
I found I made an error previously when I said that the main earth read a 'Ze' of 0.27ohm. After retesting, I believe that was actually one of the bonding conductors. Both have a similar low reading <0.30ohm.
The 3rd 10mm earth in the CU, I traced tonight had it had a Ze (Ra) of 122ohms so I'm now assuming it's a rod, possibly under the kitchen floor.
I also knocked on next door both sides - this is a row of fairly small town houses with an overhead supply. Both of the neighbours have TNCS earthing arrangements (despite my customer being refused it last Friday).
Therefore, I believe I have parallel paths via the bonds to neighbours TNCS systems, an old TT rod which I can't verify easily without ripping holes in walls or kitchen flooring and the DNO refusing to install TNCS despite both neighbouring properties having it installed.
This is where TNC-S gets really ugly... The integrity of your earth is now dependant on whether neighbours fiddle with their own installations. I don't know why we don't just mandate non-conductive couplings on incoming services
Yes. I think it will be one more call to the DNO to see if they will install TNCS after all, given the fact neighbours both sides have it.
If they still refuse, it's back to plan A, install a new rod and an RCBO board. At least I now have a better understanding of the installation.
One small sticker causing so many problems!
I know we can't guess but, if I had to guess, I bet there's an earth rod somewhere, probably beneath a new porch or conservatory!
If you really want to @aliensbrains you could let us know what Ra you get on your new rod, as we like things like that :D
Finally got round to this job today. The DNO doubled down on their refusal to install PME so I fitted a new rod and RCBO board. I got an Ra of 44.5 ohms which I was pretty happy with.
Newcastle-under-Lyme
Other
If other, please explain
Possible trainee
TT or PME
Domestic Electrician Forum
Thread Tags
Tags Tags
pme
aliensbrains,
aliensbrains,