gottahugenoggin

Hi guys
Im currently at collage and new to this,so excuse me if this is a silly question or i dont use the correct terminology......so here goes.

I went to a friends house last night after another friend replaced a surface mount socket back box on the upstairs RFC.
He asked me to pop down with my MFT to check on something he wasn't sure about.
Given the chance to get my tester out,and gain some experience off i went.
His installation is a TT with no RCD protecting any of the circuits.
The RFC was on a 32A MCB wired in 2.5 T+E
The thing that concerns me is the fact that the Zs (measured on my MFT) for the RFC was (from what i can remember) was around 150 ohms giving a PEFC of 2A.

So how can disconnection times be met on a TT with no RCD when protected with a 32A MCB with a earth fault current of only 2A???

Am i missing something here or is it genuinely worrying unsafe situation?

What would be the best way forward from here? Would the best option be to fit an RCD to cover the full CU?

Bearing in mind im am not registered to carry out the work if needed,nor would i feel confident doing so.So am just asking advice to pass onto my friend.

If he chooses to get this sorted it will be by a registered sparky

Thanks in advance........Dave
 
A potentially dangerous situation which you have done well to identify,either convert to a TN system or install a 30ma RCD to cover all as a temp fix....I would not be concerned not being registered,you are obviously competant and this needs urgent attention if you cant get a registered spark in quickly.
 
Last edited by a moderator:
back in the days of the 16th, fitting a 100mA 0r a 30mA RCD front end was the way to achieve disconnection times on a TT system. nowadays, the preferred options are PME if available and/or a dual RCD or RCBO CU.
 
as wirepuller has just stated, you could split the tails and fit an up front RCD as a temporary fix. the installation would then be much safer.
 
Thanks for all the quick replies guys,ill get onto him now to sort it out asap.He said his friends a registered spark so ill speak to him directly to let him know the situation,thanks again.....Dave
 

Reply to TT Query? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
551
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
922

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
951
I am with you. Their RCD did not comply with the standard. The only one I know that does comply, though I am sure it isn't alone, is the Garo...
    • Like
Replies
10
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top