devlin maguire

Hi All hope you can define this for me TT installation 100mA RCD, is a main switch required in conjuction with this. I do not think so as a this (and all others ?) RCD conforms to BSEN 60947 so why would some think that an addition method of isolation is required ??
Dev
 
An rcd complies with 537.2.2 Devices for isolation
In my opinion it complies better, sometimes, than a double pole isolator on a domestic consumer unit 537.2.2.3


There are hundreds of thousands of installations with the same set up
They complied before and nothing has changed regarding isolation devices to alter that
 
An RCD upfront on TT's, since the 17th, is only really required if the CU is metal clad and not insulated.

As long as all the other circuits are protected by 30mA RCD. If they were installed in earthed metal conduit or similar negating the need for 30mA protection, then there would still be the need to install an RCD front end so that the 50V touch voltage is not exceeded, ;)
 

Reply to Tt rcd in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

I agree but in most domestic situations they wouldn't be on a TT and if they are then they probably wouldn't have vfd driven borehole pumps, dual...
2
Replies
29
Views
1K
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
727

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top