J25GTi
Hi,
My question is as follows -
I have recently gone to a site to replace some lighting, and before I started I noticed the fuseboard/Earth were in a bad condition so I carried out a Ze test before starting works.
With all parallel paths disconnected and just the earth electrode I got a reading of 122.4ohms.
Now this was on a day where we have just had 2.5 weeks worth of solid rain and the ground was saturated.
I believe that when the ground is dry this will raise to more than 200ohms.
But my boss is telling me to carry on with the work as if it is less than 200ohms "It doesnt matter"
Now I remember reading somewhere in bs7671 or a GN that if the earth electrod Ze is over 100ohms then a latent defect could exist and requires investigation? But I cant find it for the life of me!
Help!
Thanks