New circuits. Ra of 229 Ohms therefore the rcds are for fault protection by design. Zdb of 0.29 (10mm gas bond) so are the rcds classed as additional protection?
 
Put water with it...reminds me of a long time ago a team were putting in a gigantic earth rod. We used to put loads of salt and coke in the earth and then water it. We dug out the earth before hand and mixed it. One of the guys toward the end jumped on the "conditioned" patch and disappeared into the ground. At the time it was hilarious.
 

Reply to TT system eic minor point in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
646
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top