T
tawraste
hi all,
haven't posted for a while, but i have been here - reading and learning. i'm hoping to get a little advice on a low pfc i've come across.
a mate has been extending his bungalow, and wants the full rewire. i've gone to have a look, and i've basically done pre work checks to assess the situation.
its a TT system, and the meter on the outside of the property has recently been moved by western power. i've come along and the meter is all connected back up to the CU. polarity is ok.
bonding is all there, with 10mm on the services and 16mm main earthing conductor. earth rod method 2 comes back with 29.4 ohms.
PSC comes back with 507A, but the PFC is only 8A !
I'm wondering if this is a cause for concern and why it should be so low?
cheers guys,
tawraste