If you are rewiring the property, why not just stick 10mm bonding in and a 16mm main earthing conductor. either reposition the earth rod and see if you get a better Ra value or add another until you get a better value, If I was rewiring the property I would be inclined to install my own rod anyway as for all you know the rod that's already been installed could of been cut down in size as hit hard ground etc when it was installed.

Because that would be a waste of time and money if only 6mm is required, you might as well install 2.5mm for lighting and 16mm for cooker supplies if you are going to use that logic .

Why are you talking of installing a rod in the singular? That won't achieve anything useful, at least 2 electrodes made up of at least 2 rods coupled together would be a good starting point.
 
Because that would be a waste of time and money if only 6mm is required, you might as well install 2.5mm for lighting and 16mm for cooker supplies if you are going to use that logic .

Why are you talking of installing a rod in the singular? That won't achieve anything useful, at least 2 electrodes made up of at least 2 rods coupled together would be a good starting point.

If there is a possibilty of a PME conversion at some point it would definately be worth upgrading now though.
 
Because that would be a waste of time and money if only 6mm is required, you might as well install 2.5mm for lighting and 16mm for cooker supplies if you are going to use that logic .Why are you talking of installing a rod in the singular? That won't achieve anything useful, at least 2 electrodes made up of at least 2 rods coupled together would be a good starting point.
Because if its a rewire, surely the whole purpose of a rewire is to rewire the whole property and no leave in the existing.And I installed a single rod a few weeks ago and got a value of 15ohms so what would be the point if installing another rod in this case?
 
Ooops, I appeared to have stirred a hornets nest.

I've fitted the installation with 30Ma RCBO's to all circuits, but so far I've left the main 100Ma RCD in the installation.

To comment on another post, about putting TWO earth rods in, I was told in no uncertain terms that this was a highly dangerous practice, and any fault going to earth would go to both rods and this would cause a dangerous potential difference, possibly resulting in a fatal shock to anyone standing near the rods at the time. The example given at the time was grazing cattle during an electrical storm, with the lighting taking the path of least resistance through the animal, rather than along the ground?

I have to confess, that I remember a figure of 200 ohms being a realistic maximum on a customer supplied rod, and any higher readings than that "required investigation"
 
Because if its a rewire, surely the whole purpose of a rewire is to rewire the whole property and no leave in the existing.And I installed a single rod a few weeks ago and got a value of 15ohms so what would be the point if installing another rod in this case?

The point of installing multiple rods is to achieve good depth and ensure stability.
The ground is generally pretty wet at the moment so your 15ohms will rapidly disappear in the summer if it is based entirely on the moisture content of the topsoil.
 
Ooops, I appeared to have stirred a hornets nest.

I've fitted the installation with 30Ma RCBO's to all circuits, but so far I've left the main 100Ma RCD in the installation.

To comment on another post, about putting TWO earth rods in, I was told in no uncertain terms that this was a highly dangerous practice, and any fault going to earth would go to both rods and this would cause a dangerous potential difference, possibly resulting in a fatal shock to anyone standing near the rods at the time. The example given at the time was grazing cattle during an electrical storm, with the lighting taking the path of least resistance through the animal, rather than along the ground?

I have to confess, that I remember a figure of 200 ohms being a realistic maximum on a customer supplied rod, and any higher readings than that "required investigation"

Were they SPSN RCBOs or are they the standard SP RCBOs which are commonly available?

Was the person who told you that 2 rods is dangerous certified as insane or something? The whole country would be in serious trouble if this was the case!

Every DNO supplied earth will have many many rods connected in parallel!
 
Ooops, I appeared to have stirred a hornets nest.

I've fitted the installation with 30Ma RCBO's to all circuits, but so far I've left the main 100Ma RCD in the installation.

To comment on another post, about putting TWO earth rods in, I was told in no uncertain terms that this was a highly dangerous practice, and any fault going to earth would go to both rods and this would cause a dangerous potential difference, possibly resulting in a fatal shock to anyone standing near the rods at the time. The example given at the time was grazing cattle during an electrical storm, with the lighting taking the path of least resistance through the animal, rather than along the ground?

I have to confess, that I remember a figure of 200 ohms being a realistic maximum on a customer supplied rod, and any higher readings than that "required investigation"

The 100ma RCD needs to be S type in order to achieve discrimination. If you have installed SP RCBO's then you will need to keep the up front S type as SP RCBO's are not recommended for TT systems.
 
surely if your hitting 180 ohms regularly then your using twigs?

are you using the rods that can be extended about 16mm ish thick (1/2" is 12.5 so around 16mm for 5/8 off the top of my head)


(got myself confused converting lol, im more used to 6/8 razors)
 
Last edited:

Reply to TT system main bonding CSA? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
779
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top