Guest viewing limit reached
Haven't got books with me but thought tt was 200 ohms tns 0.8. And tnc-s. 0.35. Sure it's in on site guide certainly that in my head lol
Thats not right mate. The IET state that in excess of 200 ohms can be unstable. As others have said you should be looking for as low as figure as possible.
I'd guess that 180 ohms now will exceed 200 ohms at other times of the year - and I ain't a betting man!
OP - I'd bend over and be ready to be well and truly spanked by Eng54 when he reads your post. At present he's getting his butt handed to him on a plate by the Yanks :)
Nope, no max value for TT systems stated.
200 ohms is suggested as a value above which Ra may not be stable.
0.8 for TNS, 0.35 for TNCS and 21 for TT are the values that a DNO will quote as the typical maximum values for each supply.
If I remember rightly, it does say in the guidance note 3 any reading over 100 ohms would be considered unstable. But it has been a while since I been in the books
If you are rewiring the property, why not just stick 10mm bonding in and a 16mm main earthing conductor. either reposition the earth rod and see if you get a better Ra value or add another until you get a better value, If I was rewiring the property I would be inclined to install my own rod anyway as for all you know the rod that's already been installed could of been cut down in size as hit hard ground etc when it was installed.
The regulations state that the value of Ra should be as low as practicable,and that an Ra exceeding 200 ohms may be unstable (table 41.5 note 2). Assuming earth fault protection is by 30ma RCD then in theory an Ra of 1667 minus the maximum value of R1+R2 on the installation would comply with Bs7671. This clearly leaves the whole thing open to interpretation.I would point out again though that in the event of an earth fault,assuming 30ma RCD protection,the outcome will be no different whether the OP's install remains at 180 ohms,or is improved to a 'stable' 20 ohms.
This is where Bs7671 fails miserably.On one hand it is implying that only sub 200 ohms readings are acceptable...and yet potentially readings far in excess of 1000 ohms will still meet the requirements.
Personally i can see no advantage at all in improving 180 ohms to 20 ohms and nobody on here has ever given a satisfactory explanation as to what 20 ohms will do that 180 wont. If you are going to improve it then the regulations should require readings approaching TN values,and if you cant accept higher values then you have to accept nothing less than TN values on your TT installations.
Crowthorne
TT system main bonding CSA?
Falcon Flyer,
Dan,